    Question water chiller question



    I have a question about water chillers.
    I want to build up a 7Kw water chiller.
    I am building a small water tank with glycol, the glycol will be cooled by a brazed plate heat exchanger using refrigerant as the primary cooling.
    In that tank I want to run a length of 3/8" copper pipe in that tank to cool down water running to another application.
    Does anyone have information on how to work out the total length of pipe i will need



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: water chiller question

    You are going to have to provide a lot more information before any calculations can be done, such as:

    What are the expected cooling water entering and leaving temps (T1, T2)

    How big is the load you are cooling

    What temp is the refrigerant evaporating at

    How much water is in the tank

    What concentration is the glycol

    What will the primary circuit flow rate be in kg/s

    What will the secondary flow rate be in kg/s

    etc

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: water chiller question

    If you are into a bit of calculation then you could start here...

    http://en.wikipedia.org/wiki/Heat_transfer_coefficient

    also
    http://www.eng-tips.com/viewthread.c...=171100&page=1
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  2. Water chiller help
    By ultralo1 in forum Trouble Shooting
    Replies: 6
    Last Post: 12-05-2007, 11:52 AM
  3. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  4. Water Chiller Control
    By David PS in forum Air Conditioning
    Replies: 4
    Last Post: 29-08-2006, 11:14 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •