    sabroe overheat smc 112 L
    hello fellow members. just registered here at re. we just purchased a sabroe smc 112L and are encountering overheating of the unit , resulting in the compressor shutting down. maybe you could recommend some reading materials which colud help me with our problem. our immediate ,easure to prevent compressor overheating is to dump the return water to the basin of the cooling tower. thanks
    Somerset
    69
    4,697
    Re: sabroe overheat smc 112 L
    Quote Originally Posted by engrp View Post
    Welcome engrp.
    Basically there are 2 main reasons for the head cooling water overheating.
    1) worn discharge valves resulting in higher than normal head temperatures.
    There are several other things that can also give this effect.
    But the above is the most common.
    2) Poor flow of the head cooling water across the heads..
    Resulting in high head temperatures due to lack of cooling.
    Several things can cause this ...
    Pump Failure ( I presume the cooling water circuit is pumped)
    The more common issue arises when the cooling tower water is used to cool the heads. Is Chemically
    treated,
    When the heads get hot and the flow rate drops off.
    The dissolved solids in the water come out of suspension..
    The resultant grey sludge clogs the water cavities in the heads...
    Further reducing the cooling effect and causing more dissolved solids to drop out of suspension...
    A vicious circle...
    TO SUMMARISE..
    Look at whether it's Mechanical or poor heat absorption..
    Either of these May be the cause???
    Just an after thought .. you are actually seeing high discharge temps and it's not the temp stat at fault??
    Mar 2008
    philippines
    61
    95
    thanks for the reply, grizzly. anyway, defect was traced to restricted water supply. thanks again.anyway, how do i post a new message ? i can't get to the blank message board
    Mar 2008
    philippines
    61
    95
    may i also ask if you can point me to a website, or can any of our fellow members share a manual for an old frick 9 x 9 compressor ? we are still using 2 of these units. thanks
    Somerset
    69
    4,697
    may i also ask if you can point me to a website, or can any of our fellow members share a manual for an old Frick 9 x 9 compressor ? we are still using 2 of these units. thanks
    What's the Model no?
    I don't recognise 9x9
    It is usually expressed as 2 or 3 letters!
    I might be able to help.
    Mar 2008
    philippines
    61
    95
    greetings, again. grizzly. i am referring to the old style reciprocating frick compressors, which may be older than you are.i will attach a picture of the said compressor. i will send in a separate reply, once i get to know how to attach a picture. thanks again
    Mar 2006
    Philippines
    124
    engrp,
    Try GNQ they might have manual for your compressor.
    Regards,
    Guapo
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, engrp
    try here...
    Quote Originally Posted by NH3LVR
    Go to http://www.frickcold.com/Products.as...lay=30&View=ON
    They have a great deal of literature online.
    Best regards, Josip
    Aug 2005
    5,302
    Quote Originally Posted by grizzly
    It's the modern version of the avatar you use grizzly.
    A 9 X 9 compressor usually consists of 2 vertical cylinders that have a 9" bore & a 9" stroke. The are single acting compressors, where your avatar is probably double acting (compresses on both sides of the piston stroke).
    Jul 2007
    Czech
    61
    373
    Hi Engrp,
    series HDI ?
    May 2006
    India
    82
    1,013
    Hi engrp,
    I will have to hunt through my old documents. Maybe I can locate the Frick 9 x9 catalog. I remember it had the complete series of 4 x 4 etc. These used to be very much in use in the 60's with ammonia refrigerant. They were very efficient. These compressors were what Iceman has described. It is the bore and stroke in inches.
    May 2006
    India
    82
    1,013
    Hi engrp
    Please download from the following link. Do so within 7 days.
    http://download.yousendit.com/370CC13C62C68C1F
    Aug 2005
    5,302
    Samarjit,
    The link you posted goes directly to a different website??? Can you provide some more detail on where to find this document please?
    Thank you.
    May 2006
    India
    82
    1,013
    I do not know how this is happening. I shall download the file again and post it.
    May 2006
    India
    82
    1,013
    Please try this link to download.
    http://www.mediafire.com/?wbfxd0cgj2m
  1. Sabroe 202 LM
    By nh3wizard in forum Industrial Compressors
    Last Post: 10-03-2011, 05:35 PM
  2. New Sabroe (Frick) Screws
    By Andy in forum Industrial Compressors
    Last Post: 21-05-2008, 04:28 PM
  3. Sabroe TSMC108S
    By guidel in forum Industrial Compressors
    Last Post: 13-06-2007, 10:38 AM
  4. sabroe water chiller
    By dill in forum Air Conditioning
    Last Post: 17-12-2006, 07:26 PM
  5. Sabroe CMO28 mk2 comp unloaders
    By GENGUS in forum Technical Discussions
    Last Post: 17-11-2006, 01:18 AM