    pjauff's Avatar
    pjauff Guest
    Pipe temp vs. fluid temp / Thermocouple install
    Hello,
    Suppose if I were to measure outside surface pipe temperatures with a contact thermocouple (wrapped in duct tape or something), how accurate would this be in a 1/4" copper pipe? I'm trying to save some time for my degree project and was wondering if this is a viable option.
    If not, does anyone have an idea how to get a thermocouple inside of a pipe cheaply? I was originally going to use these special NPT pipe thermocouples but they were too expensive
    Regards,
    Patrick
    Split Croatia
    57
    6,151
    36
    Re: Pipe temp vs. fluid temp / Thermocouple install
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    if using contact thermocouple then try using heat sink paste this will improve both response and accuracy. If you need to prove accuracy then I suggest mapping your thermocouple to known temperatures.
    pjauff's Avatar
    pjauff Guest
    Thanks for your responses, I'm going to try the heat sink paste.
    How would I go about mapping the thermocouple to a known temp? I'm unfamiliar with this.
    11,025
    Start with boiling water, 100°C, 212°F and melting ice 0°C, 32°F.
    Calibrate your sensors/thermometer to those two temperatures and you should be OK.
  1. Compressor loading, cooling, and range of operation.