    Red face YORK Chiller Air Ingress on Shutdown



    Hi,

    We are facing air ingress problem on one of our Centrifugal York chillers Model No. YTH3J3E35COG, 500 Tons with R123. Last time we found some leakage in the solenoid purge valve on the purge unit which was afterwards rectified. The purge unit was separated from other system and Vacuum was held for 24 Hours in both systems. After this satisfaction the gas was charged and chiller taken in service. After purging air from the system during the operation, the chiller worked fine at 0 purges/hour for the last 40 days. however when it was turned off, the condenser and evaporator pressures started to increase gradually and after 2-3 days time the condenser pressure reached 14.7 PSIA. Which shows an air ingress in the system.
    The problem is that the air ingress problem comes only when the chiller in non-functional (in off state). While running there in no air ingress and no purges. Can someone identify the root cause of this problem? Please let us know the efficient and quick way to detect the leakage.
    Last edited by imranmd; 11-03-2008 at 03:33 PM.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: YORK Chiller Air Ingress on Shutdown

    Have you looked at the shaft seal ?

    Just a thought!

    Grizzly

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: YORK Chiller Air Ingress on Shutdown

    Is it air leakage or refrigerant leaking through somewhere ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: YORK Chiller Air Ingress on Shutdown

    What are the ambient temperatures?

  5. #5
    Join Date
    Apr 2007
    Location
    Pakistan
    Age
    48
    Posts
    9
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    I dont think its the shaft seal as the unit was pressure tested the last time air leakage was rectified. Can anybody suggest an effective method/procedure for leak detection???

  6. #6
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: YORK Chiller Air Ingress on Shutdown

    Hello imran the exhaust valve might be faulty or the pressure transducer , just a thought

  7. #7
    Join Date
    Apr 2007
    Location
    Pakistan
    Age
    48
    Posts
    9
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    Please let me know the efficient way to detect the leak in the system. We have waisted a lot of time in detecting the leak but still experiencing the same problem. During operation the gas may leak from condensor side therefore chiller runs on zero purges and on shutdown it losses vacuum, just a thought. Please help.

  8. #8
    Join Date
    Apr 2007
    Location
    Pakistan
    Age
    48
    Posts
    9
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    Can anybody reply me earlier?

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: YORK Chiller Air Ingress on Shutdown

    Do you have any isolation valves on that system, If not, install few and isolate system parts, vacuum every part of system until 300 microns and look in rise of pressure. That way you should be able to locate part of system that is leaking. Then, depending of system components in that section of system refit any possible leaking part one by one and every time make this test. First start with devices who are sensitive at negative pressure (Schraeder valves and similar).
    You didn't answered what are the ambient temperatures there.

  10. #10
    Join Date
    Apr 2007
    Location
    Pakistan
    Age
    48
    Posts
    9
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    Thanks for your reply. Now a days the ambient temperature varies in between 27 to 33 C

  11. #11
    Join Date
    Mar 2008
    Location
    New York
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    recover the refrigerant, blank off the rupture disk, pressurize the chiller at about 20psig with r22 traceand dry nitrogen, drain the chiller and condenser and isolate just to see if may be you have a tube leaking, also what type of detector are you using, usually suction elbow gaskets are leakers and check that shaft seal is the drain cup full? do you get an indication at the shaft, check all flared connections for oil recovery eductors

  12. #12
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    395
    Rep Power
    18

    Re: YORK Chiller Air Ingress on Shutdown

    Imranmd
    I do not think it is only leaking when it is shut down I beleive it is leaking all of the time but as the air purger only works when the plant is running you are not noticing the problem when running as the air is being removed which is quite normal. However when the plant is shut down a large amount of air is being drawn in and then when you start the plant that has to be got rid of which makes the small problem look worse. I am trying to remember what the acceptable number of air purges is, one every 5 or 6 minutes rings a bell.

    It may be worth letting the plant run and check the oil pressure as if that is not high enough the purger will not work correctly either, 20PSI rings a bell.

    Long time since I worked on centrifs but still love them.

    Ian

  13. #13
    Join Date
    Apr 2007
    Location
    Pakistan
    Age
    48
    Posts
    9
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    If the leakage is at evaporator side (suction Elbow)then purges should be observed during running also. If the condensor or evaporator tubes are leaking then water should be mixed in refrigerant gas, please let me know the way to detect the leakage in tubes if any.

    Please let me know the gasket material and type at suction elbow.

  14. #14
    Join Date
    Sep 2006
    Location
    Ireland
    Posts
    37
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    imranmd,when the chiller is running the condenser is above atmospheric pressure 50 -60 kpa . it is leaking r123 out when it is running. when it cycles off both sides of system are in a vacuum and it starts sucking in air. it will need to be purged.
    i suggest first trying an ultra sonic leak detector, it will listen to the air sucking in. purge the chiller, run on a low load and continue purge till it is free of air, then shut it down and concentrate on hi-side of system start listening for leaks. if that fails , pull the charge out and blank the rupture, pressure up to 20 psig and do the same . failing that you may have a tube leak.....

  15. #15
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: YORK Chiller Air Ingress on Shutdown

    Hi Centrifs, you dont need to blank out the ruputure disc you can run a line to its outlet if it has a threaded coupling on it from the vessel and it will be eqauliazed the same pressure both sides have done it many times

    Regards Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  16. #16
    Join Date
    Jan 2007
    Location
    Portsmouth
    Age
    60
    Posts
    8
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    We once had the same problem when I worked for York, working on a 1000 Tonner in IBM Portsmouth. We Isolated the main Condenser and Chilled water Valves and introduced warm water into the Evap and Condenser slowly raising the pressure until we achieved a positive, then we took our time and found lots of leaks all told, on flare nuts, the casing, old capillary lines etc, we replaced all the lines and flares for new and re-pressure tested then ran the machine with no further problems. The Kit we used was basically a Shower unit and a pump and a pressure switch to cut it of at whatever pressure desire. Took away all the fun tho no more surging!!

  17. #17
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Re: YORK Chiller Air Ingress on Shutdown

    Quote Originally Posted by Taffy View Post
    We once had the same problem when I worked for York, working on a 1000 Tonner in IBM Portsmouth. We Isolated the main Condenser and Chilled water Valves and introduced warm water into the Evap and Condenser slowly raising the pressure until we achieved a positive, then we took our time and found lots of leaks all told, on flare nuts, the casing, old capillary lines etc, we replaced all the lines and flares for new and re-pressure tested then ran the machine with no further problems. The Kit we used was basically a Shower unit and a pump and a pressure switch to cut it of at whatever pressure desire. Took away all the fun tho no more surging!!
    Was that in Portsmouth itself or in Cosham taffy....brings back memories....anyway...good suggestion...we used to carry out a service/change filters etc in R11 centrifs (Yorks/Carrier etc) by utilising the building hot water supplies (with clients permission)....just had to take a hose and connect it to a tap in the boiler room..valve off the unishell and allow a drain flow at the same rate as the water flow in...saved all that hefting heavy drums and getting your brain buzzing and your nose running when working on units in basements and having to remove the complete charge...although it sure did clear your head when you had a cold lol
    Last edited by Superheatman; 30-07-2008 at 08:13 PM. Reason: wrong word
    Not getting wiser at the same rate as I am getting older??

  18. #18
    Join Date
    Aug 2008
    Location
    UAE
    Posts
    5
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    York YT chillers had 2 purge units options: The Turboguard and the Skyguard. The turboguard cannot remove condensables when the chillers is idle but the skyguard can. Based on your description of the problem I think you probably have the turboguard version so it might be better for you to upgrade to the skyguard version. At least it will remove the non-condensables when the chiller is off.

  19. #19
    PRESLAV's Avatar
    PRESLAV Guest

    Re: YORK Chiller Air Ingress on Shutdown

    Quote Originally Posted by dbobo View Post
    York YT chillers had 2 purge units options: The Turboguard and the Skyguard. The turboguard cannot remove condensables when the chillers is idle but the skyguard can. Based on your description of the problem I think you probably have the turboguard version so it might be better for you to upgrade to the skyguard version. At least it will remove the non-condensables when the chiller is off.
    HELLO MY FRIEND. I am from bulgaria - eastern europe. I work in place where is a hermetic turbopack compressor from YORK . HE has a sistem TURBOPACK which is to come out the air from the sistem filled with *****. Yes but yestarday when TURBOPACK works he come out not air but real liquid ***** and oil mixxed . It was fun because we where there and all ***** come all over us. We cant understand where is the problem and how turbopack will come out liquid ***** and oil but not air gas. what do you think where can be the problem. I can give you more info if you are intrested. The york compressor is from 1988 year i think.

  20. #20
    pbreden's Avatar
    pbreden Guest

    Re: YORK Chiller Air Ingress on Shutdown

    Hey Buddy..... 1998 is not that old! Sorry that you have been covered with that suff, don't lay out for a year or smth!! Pls. be more specific if you can cause it's not easy to determine.... Is it a closed system or a large piping system????????

  21. #21
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: YORK Chiller Air Ingress on Shutdown

    the problem is hand high pressure (condenser, lubrication, mechanical seal) since as mention during unemployment pressure condenser becomes negative, passes the machine put 10 lbs of nitrojeno (psig) and that this machine without oil for q sign where this problem

  22. #22
    lpertuz's Avatar
    lpertuz Guest

    Re: YORK Chiller Air Ingress on Shutdown

    hola disculpen les hable en espaņol soy de venezuela caracas, tengo a mi cuidado un chiller similar y me sucedia lo mismo lo que debes hacer es lo siguiente:
    1: verificar posible entras de aire
    2: hacer una parada y hacerle mantenimiento al zoom de purga y reemplazar el filtro de prepurga y purga.
    3: cambiar la unidad de filtrado de cartuchos en baja y autolimpiante y aceite.
    4: apretar las tornillos de la boluta tienden a aflojarse y a aspirar aire.
    5: verifica estado de torres y condensador producto de obstrucciones eso es un factor para ese problema

  23. #23
    Join Date
    Jul 2006
    Location
    Israel
    Age
    84
    Posts
    11
    Rep Power
    0

    Re: YORK Chiller Air Ingress on Shutdown

    This sounds like a shaft seal problem, the fact that this happens on shut down supports this.When the compressor is running I imagine the pressure is high (oil pressure )

  24. #24
    Join Date
    Sep 2008
    Location
    Newcastle upon tyne
    Age
    75
    Posts
    80
    Rep Power
    16

    Re: YORK Chiller Air Ingress on Shutdown

    Hi \
    I agree with Taffy, put hot water into chiller water side after isolating valves
    We use a Reftec unit to circ hot water
    with a good electronc leak detector u should be able to find something. was very good recently on a TRANE 3 stage with motor terminal box plate leaking. Other advantage is u dont need nitrogen and with a good mechanical type purge, u can start machine and get it straight up to load.

    AWW

    See this is an old thread but info relevant
    Last edited by alan wolf; 02-04-2010 at 12:52 PM.

Similar Threads

  1. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  2. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. york chiller not running
    By cool it in forum Trouble Shooting
    Replies: 21
    Last Post: 16-06-2006, 12:13 AM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 24-03-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •