    Hi All... I am New here and I could really use some help...



    Need second opinion for this Carrier Unit I am working on.

    Hi... I am Dave, and I am new here

    I guess you can say that I am second guessing myself here and I am slightly embarrassed.. But I need some help... And here is what I need from you all if it is possible.....

    I am a certified A/C and Heating Technican... I graduated from RSI, (Refrigeration School Institute),Institute in Phoenix.. I am asking for a second opinion of which the first is my opinion... But I need your help if at all possible...

    I have a Carrier roof top, A/C and Heating unit that has a Mother Board, (Control Board)... This board has an Error code detection light when something is wrong... It flashes 1 thru 8 error codes.... Now the particular errors are as follows... It listed 3 errors...
    The inducer fan will not shot off to complete the shut down cycle after it reaches the Thermostat setting…. As the fan just keeps running until I turn off the main power. These are the error codes that are displayed on the Board before I shut off the main power…

    1 flash.... Fan on/off delay modified
    6 flashes.. Inducer switch fault
    8 flashes.. Internal control fault

    I have never had a unit show so many errors codes... But my opinion is that the Mother Board,(Control Board),is at fault and I need another Mother Board, (Control Board). Because the Fan Delay is internal to the board and also the Internal Control Fault is also part of the Board, and I also believe that the Inducer Control switch is also part of the board.... Can you confirm that I need a new board??? I do not want to replace the board with out a your advice first....

    Carrier Roof Top... A/C n Heating unit

    Model #..... 48SS-042080321
    Serial #.... 4695G80613

    Thank You,
    David Morton...





  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Hi All... I am New here and I could really use some help...

    On a call for heat if limit sw. and rollout sw are closed igc safty logic will initiate ignition sequence then the ignition hi voltage transformer will create a 10,000 volt spark for 5 seconds and the gas valve will be open for 5 seconds if you get the burner on watch to make sure it doesn’t shut down on the limit switch but only on the thermostat
    Go to page 81
    http://www.docs.hvacpartners.com/idc.../48_50a-6t.pdf