Results 1 to 50 of 95
13-04-2008, 01:30 PM #1
13-04-2008, 06:33 PM #2
Re: TXV's To Adjust or Not to Adjust - That is ....
If the fans are not runing and the valve closes, what difference does it make which orfice size is installed? Closed is closed. If the coil is flooding the valve should respond unless the piping arrangment and bulb location permit flow through the bottom of the suction pipe without cooling the bulb.
There will be little or no superheat to open the valve.
13-04-2008, 07:32 PM #3
Originally Posted by Refrigerologist
It might seem like you opened Pandoras box, but I don't think so. These are the types of discussions that once in print help to support learning for others.
The only down side in setting the TXV's to control the total superheat is that now the compressor bodies may sweat or have frost on them depnding on the application. Then someone thinks the compressor is flooding back and resets the TXV's so the compressors run HOT AGAIN!If all else fails, ask for help.
13-04-2008, 07:35 PM #4
Originally Posted by NH3LVRIf all else fails, ask for help.
13-04-2008, 07:45 PM #5
13-04-2008, 08:01 PM #6
This is the only way I can think of where the valve might tend to leak liquid sometimes (although I don't think it would not be a great amount by any means).If all else fails, ask for help.
Everything You Need To Know About TXV's
By marc5180 in forum FundamentalsReplies: 12Last Post: 06-03-2008, 11:12 AM -
How to test TXVs' capacity
By liujunwei in forum FundamentalsReplies: 3Last Post: 28-01-2008, 09:03 AM -
How to adjust head on a water cooled condenser
By kengineering in forum Technical SpeculationsReplies: 5Last Post: 30-05-2007, 10:37 PM -
Basics of TXV's
By US Iceman in forum FundamentalsReplies: 5Last Post: 21-05-2007, 03:27 PM -
heat pump capacity adjust
By Lc_shi in forum FundamentalsReplies: 5Last Post: 14-02-2006, 07:32 AM