Results 1 to 50 of 95
11-03-2008, 03:45 PM #1
Re: TXV's To Adjust or Not to Adjust - That is ....
I just remembered something due to NH3LVR's comments on ammonia TVX's. How often do you rebuild or replace ammonia TXV's?
For people who work on ammonia systems this is the result of a very common issue called wire-drawing. Ammonia TXV's are very prone to this and the result is the pin and seat wear away. Eventually the valve orifice is worn out and can't control the liquid flow for superheat control anymore.
Adjusting an NH3 TXV with this problem is a waste of time.If all else fails, ask for help.
Everything You Need To Know About TXV's
By marc5180 in forum FundamentalsReplies: 12Last Post: 06-03-2008, 11:12 AM -
How to test TXVs' capacity
By liujunwei in forum FundamentalsReplies: 3Last Post: 28-01-2008, 09:03 AM -
How to adjust head on a water cooled condenser
By kengineering in forum Technical SpeculationsReplies: 5Last Post: 30-05-2007, 10:37 PM -
Basics of TXV's
By US Iceman in forum FundamentalsReplies: 5Last Post: 21-05-2007, 03:27 PM -
heat pump capacity adjust
By Lc_shi in forum FundamentalsReplies: 5Last Post: 14-02-2006, 07:32 AM