Re: TXV's To Adjust or Not to Adjust - That is ....
Originally Posted by Refrigerologist
It might seem like you opened Pandoras box, but I don't think so. These are the types of discussions that once in print help to support learning for others.
The only down side in setting the TXV's to control the total superheat is that now the compressor bodies may sweat or have frost on them depnding on the application. Then someone thinks the compressor is flooding back and resets the TXV's so the compressors run HOT AGAIN!If all else fails, ask for help.