    Re: TXV's To Adjust or Not to Adjust - That is ....

    [quote=philfridge;100895]
    Quote Originally Posted by Refrigerologist View Post
    Many engineers' in this industry say "you should never adjust a TXV superheat setting as they are factory set".

    This is correct and if you select the right size orifice no adjustment is required . Its all about knowledge and experience , however not everyone knows how to select the correct size orifice they then start messing with the t.e.v ?? why o why just leave them valves alone and get some training
    If you read some of my previous posts you will see that I completely disagree. Valve superheat should always be checked and adjusted as per individual system requirements. As I have said, if we are not to adjust the valve then the manufacturer would not bother to fit an adjustment screw I would suggest you look at a selection catalogue for, say Danfoss valves, it will show that an orifice will provide different capacities at differrent conditions and the valve cannot be factory set to cover all of the possible conditions that the valve will need to cover!
    Last edited by Refrigerologist; 10-04-2008 at 07:59 PM.

  2. #2
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Thumbs down Re: TXV's To Adjust or Not to Adjust - That is ....

    [quote=Refrigerologist;101113]
    Quote Originally Posted by philfridge View Post

    If you read some of my previous posts you will see that I completely disagree. Valve superheat should always be checked and adjusted as per individual system requirements. As I have said, if we are not to adjust the valve then the manufacturer would not bother to fit an adjustment screw I would suggest you look at a selection catalogue for, say Danfoss valves, coit will show that an orifice will provide different capacities at differrent conditions and the valve cannot be factory set to cover all of the possible conditions that the valve will need to cover!
    Like i said you do not need to adjust the valve if you know what you are doing with orifice selection . As you mentioned Danfoss valves these are preset at 2 1/2 turns out and this does not need any adjustment in my experience

  3. #3
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: TXV's To Adjust or Not to Adjust - That is ....

    [QUOTE=philfridge;101154]
    Quote Originally Posted by Refrigerologist View Post
    Like i said you do not need to adjust the valve if you know what you are doing with orifice selection . As you mentioned Danfoss valves these are preset at 2 1/2 turns out and this does not need any adjustment in my experience

    I completely disagree, comparing a danfoss tuae valve which has 9 selectable orifice sizes to say a sporlan balanced port valve (SBF series) which has only 5 - leaves a lot of room for mismatching evap load to valve capacity with the sporlan valve. If you believe EVERY single valve will keep 6K superheat then maybe you need to set up some more evaps... distributor and coil design have a big influence on how a valve behaves as well - this is why every valve should be evaluated for its performance and adjusted if necessary to keep a stable superheat.

    I commission supermarket cases nearly every day (or night ) and have been doing so everyday for nearly 8 years straight now and I cannot tell you how many of the same cases with the same evaps, distributors and txv's I come across... if you think they all behave the same as far as superheat control you have another thing coming. I use an Einstein or RMCC in a suitcase and setup probes to log and graph their performance, there are differences in their factory setting to say the least, Alco valves are the worst as far as differing behaviours for the same given conditions, then sporlan and I'd have to say Danfoss are probably the best as far as consistency goes.

    I'd love to just start them up and skip the whole txv logging and adjusting but unfortunately the supermarkets over here have consulting engineers that will randomly check superheat in each store on handover - if its not between 4 to 6k you will be made to do them all again .
    Last edited by 750 Valve; 11-04-2008 at 01:09 PM.
    ...and she said "give it to me you big fridgie"

  4. #4
    Join Date
    Nov 2006
    Location
    Guernsey
    Age
    65
    Posts
    237
    Rep Power
    18

    Re: TXV's To Adjust or Not to Adjust - That is ....

    [quote=750 Valve;101205]
    Quote Originally Posted by philfridge View Post


    I completely disagree, comparing a danfoss tuae valve which has 9 selectable orifice sizes to say a sporlan balanced port valve (SBF series) which has only 5 - leaves a lot of room for mismatching evap load to valve capacity with the sporlan valve. If you believe EVERY single valve will keep 6K superheat then maybe you need to set up some more evaps... distributor and coil design have a big influence on how a valve behaves as well - this is why every valve should be evaluated for its performance and adjusted if necessary to keep a stable superheat.

    I commission supermarket cases nearly every day (or night ) and have been doing so everyday for nearly 8 years straight now and I cannot tell you how many of the same cases with the same evaps, distributors and txv's I come across... if you think they all behave the same as far as superheat control you have another thing coming. I use an Einstein or RMCC in a suitcase and setup probes to log and graph their performance, there are differences in their factory setting to say the least, Alco valves are the worst as far as differing behaviours for the same given conditions, then sporlan and I'd have to say Danfoss are probably the best as far as consistency goes.

    I'd love to just start them up and skip the whole txv logging and adjusting but unfortunately the supermarkets over here have consulting engineers that will randomly check superheat in each store on handover - if its not between 4 to 6k you will be made to do them all again .
    The quote at the head of your post is not one of mine. I believe valve superheat should be checked and adjsuted, if it is required, for every system on commissioning. In other words you will get no argument from me I will also add that I too find Danfoss valves to be the best and most consistent.
    Last edited by Refrigerologist; 11-04-2008 at 04:05 PM.

Similar Threads

  1. Everything You Need To Know About TXV's
    By marc5180 in forum Fundamentals
    Replies: 12
    Last Post: 06-03-2008, 11:12 AM
  2. How to test TXVs' capacity
    By liujunwei in forum Fundamentals
    Replies: 3
    Last Post: 28-01-2008, 09:03 AM
  3. How to adjust head on a water cooled condenser
    By kengineering in forum Technical Speculations
    Replies: 5
    Last Post: 30-05-2007, 10:37 PM
  4. Basics of TXV's
    By US Iceman in forum Fundamentals
    Replies: 5
    Last Post: 21-05-2007, 03:27 PM
  5. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •