    Exclamation Copper tube pitting



    Hi,
    we have installed last year ice bank tank, with direct evaporation within copper tubes.
    Everything was fine for months, and than customer had stopped production for a month.
    When they restarted the ice bank plant, suddenly they saw that bubbles and oil was coming out of the water, and realized that upper few raws are full of small holes (suroudend by green matter - probably corrosion?).

    We have installed cca 20 ice banks like that, and never had any problems.

    Anyone has an idea what might happaned or have similar expirience?

    Rio



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Copper tube pitting

    Rio
    Is the water "processed" on-site or is it what we would call Mains or Tap Water.

    The reason I ask is,because I am not sure but does not heavily clorinated water (high clorine content) attack the copper.

    Something has attacked the Copper by the sound of it.

    If the process water is re-cycled after having been used to flush and clean plate heat exchangers for instance.

    The cleaning agents used are some " Heavy Duty Chemicals!
    Just a thought!!!
    Grizzly

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Copper tube pitting

    What was the quality of the copper tube installed?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Copper tube pitting

    I've seen this when softened water (slightly salty) has been used to fill the tank.
    When they are running the ice seems to slow down the corrosion process.
    I have also had one where the manufacturer used silver solder and did not clean the flux away and this caused the joints to leak after time.
    As i'm sure you know you can get a corrosion inhibitor to put in them to protect the coil.

    Jon

Similar Threads

  1. Copper tube degreasing specification
    By Thermatech in forum Technical Discussions
    Replies: 2
    Last Post: 23-05-2007, 03:10 PM
  2. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Replies: 15
    Last Post: 03-04-2007, 08:25 PM
  3. oxidation scale in copper tube and fittings
    By DeB in forum Fundamentals
    Replies: 8
    Last Post: 23-06-2006, 09:45 PM
  4. Submerged copper tube
    By Peter_1 in forum Commercial
    Replies: 12
    Last Post: 31-05-2006, 02:21 AM
  5. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •