    R407C and R22



    What is detail different bitween R407C and R22 ?
    can we changs two gas together?
    any feedback highly welcom



  2. #2
    Hodgo's Avatar
    Hodgo Guest

    Re: R407C and R22

    What is the application? compressor? chiller? A few more clues please.

  3. #3
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: R407C and R22

    I wouldn't mix them if thats what you ment.If you want more specific readings and details,refer to the P-T Chart on the refrigerants.I take it its an Air Conditioner you're working on?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R407C and R22

    Check out the manufacturers websites for technical details of most refrigerants, such as here...

    http://www.refrigerants.dupont.com/S...s/*****22.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2008
    Location
    Melbourne, Australia
    Age
    40
    Posts
    48
    Rep Power
    0

    Re: R407C and R22

    G'day, R22 is HCFC azetrope, R-407C is HFC non-azetrope meaning it has a temperature glide as its a blend of gases and must be liquid charged. It also requires polyester oil. R-407C is one of the replacements for R22 in most new A/C equipment and chillers from 10kw to 200kw.

  6. #6
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: R407C and R22

    hassan,

    If you are inquiring about converting from R-22 to R407C follow this link to Copelands AE bulletin. The first paragraph will help with your decision.

    http://www.hvacrinfo.com/cope_ae_bulletins/95-14.PDF

  7. #7
    Join Date
    Nov 2008
    Location
    Foshan,Guangdong,China
    Posts
    22
    Rep Power
    0

    Re: R407C and R22

    it doesn't work to mix the two together.