    saving energy



    I, was a supermarket tech the last six years and made the move to critical cooling last month. Working in markets my main goal was to save energy. Floating head floating suction flooding evap coils using mechanical subcooling etc.

    Now working on a/c units, Data Aire, APC, Stulz etc the one thing I notice is these units run at a 240 head. Energy savings is not something they care about. I do understand the reason why they do this though I was wondering if you could use say a hy-sav device or some way to lower head and increase line pressure etc. Any ideas to save energy, Let me know.

    Joe



  2. #2
    gloucesterfridg's Avatar
    gloucesterfridg Guest

    Re: saving energy

    My very thoughts as I was looking at Fasthosts data centre in Glos as Denco were shoving in another load of air cooled condensers..

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: saving energy

    There is an answer
    As I understand all other types of compressors use elevated head pressures for oil return. However the new Turbocor compressor does'nt have oil and can run with a very high COP in comparison, but suffers when fully unloaded. And if the hy save device is an item which spins the fluid in liquid line it will save on efficiency - check out Vicktor Schauberger's work

  4. #4
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: saving energy

    The reason we run our head pressure at 18bar is to keep the SHR correct so we don't make the air too dry and cause server issues etc etc

    Have a look at the Psychrometric chart at the web site below.

    http://www.handsdownsoftware.com/HEATCRAFT-Chart.PDF




    So if you want to keep the room at 21 degrees and 50% RH what would be the point running the SHR low and drying the air????

    If its a cooling only system and the room does not care what the RH is at them you can set the SHR lower....

    There are better ways of saving energy.... hot isle/cold isle ..... ambicool system...... heamo system..... vapour seal....... setting the return temp higher......... etc etc


    Simples.
    Last edited by Denco Technical; 25-05-2011 at 12:37 PM.
    Rob Woodworth
    GEA Denco Technical Support
    rob.woodworth@geagroup.com

Similar Threads

  1. energy saving module
    By jess in forum New Technologies
    Replies: 17
    Last Post: 22-02-2011, 11:26 PM
  2. Energy saving bulbs & PIR sensors
    By Jez in forum Electrical
    Replies: 33
    Last Post: 23-07-2010, 01:45 AM
  3. Ammonia compressor's energy saving by inverter
    By torranin in forum Industrial
    Replies: 5
    Last Post: 23-01-2008, 12:00 PM
  4. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Replies: 5
    Last Post: 15-01-2008, 06:54 PM
  5. Energy saving
    By chemi-cool in forum New Technologies
    Replies: 17
    Last Post: 17-11-2006, 04:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •