    hi every body



    hi every body i am Ahmed living in cairo -egypt and i would like to be amember in these wonderful group, i working with AMMONIA system (from 4 months ago) and we insulated in our factory new flowfreezer ,the freezer capacity (frigoscandya) 3400 kg/hr (peas) and we have abig problem with this one that we didnot get setpoint temperature - 40c on coil which effect in freezer efficiency , also we have refrageration system (GEA system or FES system) ,we feed a surge dram tank from -6c pump package (Note that : the degree on surge dram -40c)
    i need your help to solve these problem and thanks for every one



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: hi every body

    Hello Ahmed and welcome to the forum, I'm sure that someone will be able to help with your question.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: hi every body

    Hi and welcome to the RE forums.

    The information you have provided does not help us to understand your problem.

    If you need to maintain -40C in the freezer then the suction pressure at the compressor suction should be around 0.6 bar absolute pressure. To achieve this your compressors should be running at full capacity (slide valve at 100%).

    Is the -6C vessel being used as an economizer to feed cold liquid to the -40C vessel?

    We will need additional information from you such as:
    Discharge pressure of compressors
    Suction pressure of compressors
    slide valve %

    Can you find the evaporating pressure at the evaporators for us also?

    If you can provide any data in addition to the above this will helps us to understand what you have before we start to provide things for you to check.
    If all else fails, ask for help.


  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: hi every body

    Hi, Ahmed.ragab

    Welcome to RE forums...

    Quote Originally Posted by Ahmed.ragab View Post
    hi every body i am Ahmed living in cairo -egypt and i would like to be amember in these wonderful group, i working with AMMONIA system (from 4 months ago) and we insulated in our factory new flowfreezer ,the freezer capacity (frigoscandya) 3400 kg/hr (peas) and we have abig problem with this one that we didnot get setpoint temperature - 40c on coil which effect in freezer efficiency , also we have refrageration system (GEA system or FES system) ,we feed a surge dram tank from -6c pump package (Note that : the degree on surge dram -40c)
    i need your help to solve these problem and thanks for every one

    As US Iceman said....you should provide some more data about your problem....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Mar 2008
    Location
    cairo
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: hi every body

    thanks every body for helping

    1- we have -40 pumppackage (with compressor suction pressure -8.7psig) this compressor discharge to -6c (32 psi) pumppackage (intercooler)

    2-we increases the addational freezer to our system but the amount of NH3 (in-40 pumppackage) is not enough to feed new freezer so we feeding new freezer from (-6c) intercooler which give an tank over the coil (SURGE DRAM) and dropped the pressure from 32psi(-6c) to -8.7psi (-40c) using expansion valve.

    3-the problem here that the temperature of coil on the freezer do not reach to-40c but the temperature in surge dram -40

    4-these graph my help u to can image the position

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: hi every body

    Well, I see some immediate problems.

    At -40C evaporating temperature the pressure of ammonia is 8.7 inches of mercury (in. Hg), not -8.7 psig. Therefore if you have 8.7 in. Hg suction pressure at the low stage compressor (since you said you have an intercooler) something is wrong with your pressure readings.

    If you have 8.7 in. Hg (10.41 psi absolute or 0.7 bar absolute) suction pressure the evaporating pressure in the evaporators will be higher because of the pressure loss in the piping (from the evaporators to the compressor).

    So, if the system was designed properly (and nothing else is wrong) then your evaporating pressure should be about 12.4 psia (4.7 in. Hg or about 0.8 bar absolute) or -34F (-36.6C). The suction pressure at the compressor is ALWAYS lower than the evaporating pressure (if it is the same, the compressor is not running!).

    I am not sure how you are feeding liquid to the freezers. From your description, the -40C vessel is a pump package which would mean your freezers are liquid overfeed. Is that correct?

    And, if I understand your additional comments you are feeding liquid to the freezer coils from the -6C pump package (which is also an intercooler). Is that correct?

    I am going to make a guess now.... Are your freezer temperatures about -35C or slightly higher?
    If all else fails, ask for help.


  7. #7
    Join Date
    Mar 2008
    Location
    cairo
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: dear sir

    Dear (MR-Iceman) THANKS ALOT FOR UR INTEREST:

    1- we have 2 pumppackage 1st one working at
    -40C which feeding 4 freezers and 2nd one working at -6C which feeding (air conditions, fresh cold store and chillers)

    2-the problem here that the amount of NH3 in -40 pumppackage is not enough to load it with new freezer so we load the new freezer fron -6 pumppackage which feed (SURGE DRAM) vessel which feeding directly evaporator coils of freezer

    3-we make adropp in pressure before the vessel entrace by expansion valve (from-6C to -40C).

    finally ur geuss is right that the temperature of freezer is -35 but the compressors set poins for:
    *-40C suction pressure (-8.7PSIg) and discharge pressure is (30PSIg)
    *-6C suction pressure (30PSIg) and discharge pressure (150 PSIg)

    *now i working with suction pressure -12psi to give me about-37C or -38C on the freezer coil

    Note that: i feed surge dram from -6C pumppackage but the retun vapour (ammonia) to -40 pumppackage

  8. #8
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: hi every body

    Hi Ahmed.ragab, are you sure with 3500kg/an hour? - it is not more?, much operators so works. Josef.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: hi every body

    HI.

    Quote Originally Posted by Ahmed.ragab
    2-the problem here that the amount of NH3 in -40 pump package is not enough to load it with new freezer ...
    Is your refrigerant charge too low, so you are using the liquid in the -6C intercooler?

    '''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''

    This is where I have difficulty in following your description of the operation.

    Quote Originally Posted by Ahmed.ragab
    ...so we load the new freezer from -6 pump package which feed (SURGE DRAM) vessel which feeding directly evaporator coils of freezer.
    Are you pumping liquid from the -6C vessel to the freezer evaporator coils? I do not understand what the surge drum is for.

    Quote Originally Posted by Ahmed.ragab
    3-we make a drop in pressure before the vessel entrance by expansion valve (from-6C to -40C).
    Where is the this at?

    If you are doing what I think you are doing, you are pumping liquid from the -6C vessel to the freezer coils and the hand expansion valves on the freezer coils are almost closed so that you can get a low pressure equal to -40C.

    Is that correct?
    Last edited by US Iceman; 04-03-2008 at 07:20 PM. Reason: editing
    If all else fails, ask for help.


  10. #10
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: hi every body

    Hi, Ahmed. rageb you have you got in technical documentation written evaporative temperature -40°C, 3400kg/hour, temperature deep - freezes -40°C?

  11. #11
    Join Date
    Mar 2008
    Location
    cairo
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: hi every body

    Dear sirs,
    i need ur mail to send for u some photos which can help me to explain the problem .

    (SURGE DRAM) is the vessel tank which we filled it with liquid from pumppackage (-40C)
    this SURGE DRAM feeding the freezer coil , the distance between the surge dram and coil about 1-2m , it is directily over the freezer coil

    thxs for u

  12. #12
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: hi every body

    Hi, Ahmed.ragab

    Quote Originally Posted by Ahmed.ragab View Post
    Dear sirs,
    i need ur mail to send for u some photos which can help me to explain the problem .

    (SURGE DRAM) is the vessel tank which we filled it with liquid from pumppackage (-40C)
    this SURGE DRAM feeding the freezer coil , the distance between the surge dram and coil about 1-2m , it is directily over the freezer coil

    thxs for u
    ....seems you have gravity feeding freezer coil Can you upload a scheme of your plant....it will be much easier for all

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: hi every body

    Well, if that is a gravity flooded freezer coil there can be different issues also.

    If you can reduce the photo size to less than 100 kb, then you can post it with your message. That would really help.

    Thanks.
    If all else fails, ask for help.


  14. #14
    Join Date
    Mar 2008
    Location
    cairo
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: hi every body

    ok sirs,
    this graph my help u, and i will send more photos later. plz send to me e-mail
    ths
    Last edited by Ahmed.ragab; 05-03-2008 at 01:50 PM.

  15. #15
    Join Date
    Mar 2008
    Location
    cairo
    Age
    41
    Posts
    10
    Rep Power
    0

    Re: hi every body

    hi dear sirs,
    i have anew stranger problem in acold store room,this room working with danfous valve station, the problem start from about 2 weeks,the room temperature increases to -2 or -4C, i checked the valve station and i found that the main suction valve
    (danfous PM1-65) have aproblem with opening but the solenoid valve working good, now i working with manual valve (sevice valve) and i canceled the danfous valve effect, now i need to check danfous valve but i cant because there is no service valve before the danfous valve

  16. #16
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: hi every body

    A Danfoss PM-1 is the slave section: If this is being used as a regulator, there is a pilot module threaded into the adapter that looks like the top of a Theremal Expansion Valve without a Capillary Tube. If its a gas powered valve, it has a custom reducing coupling inserted in the same adapter boss which extends as pipe or tubing to a pilot solenoid. Either way, the valve should open at least part way by means of the manual opening stem in the center of the adpater.

    If you don't have an upstream service valve, you will need to pump out the evaporator. To advise how to do that you will need to provide us some detail on the valving, and whether this is a Hot Gas Defrost arrangement or some alternate form of defrost.

Similar Threads

  1. Hello To Every Body
    By m.javadinejad in forum New to RE
    Replies: 5
    Last Post: 24-11-2007, 12:10 AM
  2. York J Body Windings
    By GHAZ in forum Industrial Compressors
    Replies: 2
    Last Post: 09-07-2007, 10:06 PM
  3. Any body got any tools lying around?
    By cold as ice in forum Tools and Calculators
    Replies: 20
    Last Post: 20-10-2006, 07:26 AM
  4. Stainless Steel Filter Body
    By Derek in forum Industrial
    Replies: 2
    Last Post: 10-04-2003, 06:25 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •