defrost thermostat closed failure
hai guys i get one problem in carrier container freezer
defrost thermostat closing failure or open failure.
i changed new thermostat,but still there is same alarm appear.
what is range of closing temperature and open temperature of thermostat. how i can check the thermostat is deffecteive or effective.
TRY TO LEARN MORE ABOUT A/C SYSTEM
-
02-03-2008, 10:21 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: defrost thermostat closed failure
Generally speaking, if you changed thermostat with new one of same characteristics and you did not make mistake when wiring it, then thermostat is not cause of error.
Also, bare in mind, that alarm is active if temperatures in controlled space is not within acceptable working conditions.
-
02-03-2008, 11:55 PM #3
Re: defrost thermostat closed failure
rkmoorthy
A common setting for these controls would be:
Fan Delay cutout at +45 F and a cut in at +25 F.
Defrost termination approx 55 F
To determine what you have would require the Brand and model number of the evap and the type of control you have.......... 2 wire, 3 wire, snap disk or adjustable.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Toshiba RAV SM/SP1400 defrost problem
By SteinarN in forum Heat PumpsReplies: 11Last Post: 20-02-2008, 05:25 PM -
No Power for Defrost Timer Motor
By kln in forum DomesticReplies: 6Last Post: 21-01-2008, 09:22 AM -
Compressor thermostat failure
By Rickspain in forum Air ConditioningReplies: 5Last Post: 11-01-2008, 10:08 PM -
Why do they ice up?
By Abe in forum DomesticReplies: 9Last Post: 15-04-2002, 03:42 PM