    Talking mixing 404 wit 502



    i have this ice machine tht needs sum gas just like 1lb or 1/2lb and i was just wondering if i can mix those two refrigerant wit out effecting the sytem and if will work fine ????



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: mixing 404 wit 502

    Why would you mix gases? Is there any justified reason to do that, except wish to do it quick and leave even quicker.

  3. #3
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: mixing 404 wit 502

    I was under the impression that mixing refrigerants was illegal in the US.

    Its not a good idea anyway.

    if its running on r502 you can top up with r408a but i didnt tell you that.

  4. #4
    Join Date
    Apr 2002
    Location
    scotland
    Posts
    114
    Rep Power
    23

    Re: mixing 404 wit 502

    what he says ^
    you may even get away with adding R22. R404A is not compatible with the mineral oil used in R502 systems. The ideal scenario is to recover the existing charge, fix the leak (if there is one) change the drier and recharge with R408 - not forgetting to vac out etc etc

  5. #5
    Join Date
    Mar 2008
    Location
    usa
    Posts
    9
    Rep Power
    0

    Re: mixing 404 wit 502

    well the ice machine has 404

  6. #6
    Join Date
    Mar 2008
    Location
    usa
    Posts
    9
    Rep Power
    0

    Re: mixing 404 wit 502

    u think because the machine has 404 and it just need a little bit of gas

  7. #7
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: mixing 404 wit 502

    you are saying it is on r404 but you want to put r502 in it.

  8. #8
    Join Date
    Mar 2008
    Location
    usa
    Posts
    9
    Rep Power
    0

    Re: mixing 404 wit 502

    sum yea maybe 1/2 lb

  9. #9
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: mixing 404 wit 502

    Dont you have any r404a?

    no you cannot mix r404 and r502 because of the oil.

  10. #10
    Join Date
    Mar 2008
    Location
    usa
    Posts
    9
    Rep Power
    0

    Re: mixing 404 wit 502

    so and the only thing tht i can top this charge off is only wit 404 i cant use any other refrigerant wit out doing any other type of changes ???

  11. #11
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: mixing 404 wit 502

    no there isnt any other gas you can mix with 404.so ideally you need to get hold of some.

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: mixing 404 wit 502

    What are you doing with R502????

    No 'topping off' ffs. Recover charge. Fix leak. Pressure leak test. Vac out. Recharge.
    If you have not the skills and/or tools to do this get a profesional in.
    It may not even be short of charge but have a blockage somewhere, adding refrigerant in this case will be ineffective at best and dangerous at worst.

  13. #13
    Join Date
    Mar 2008
    Location
    usa
    Posts
    9
    Rep Power
    0

    Re: mixing 404 wit 502

    i think them i need to get a hold of 404 thx bro :O)

  14. #14
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: mixing 404 wit 502

    Quote Originally Posted by monkey spanners View Post
    What are you doing with R502????
    Very good point! where did you get it from?
    With it being an ice machine you will have to have proper R404 with no mixing and the exact charge or else it will not work.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: mixing 404 wit 502

    First, you are trying to mix azeotrope with zeotrope refrigerant. Second, if you do that, you came up with unknown mixture of unknown properties. Factory refrigerant mixtures are precisely combined to have certain characteristic. If you change that composition you could not be sure that is going to work satisfactory and chance that you could end up with same result as non condensables are pretty high.

  16. #16
    Join Date
    Mar 2008
    Location
    usa
    Posts
    9
    Rep Power
    0

    Re: mixing 404 wit 502

    yea i got tools and all tht i was just wondering if i can do it skills well as you can see i am new but im a fast learner and mixing 502 wit 404 was a question tht i had and thx for all your meseges
    :O)

  17. #17
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: mixing 404 wit 502

    Mixing = YOU FAIL

    Topping up with out fixing leak = YOU go to jail if cuaght.

    Not worth it IMO.

    Use proper perceduar, if you do not know proper percedure (As the question in of its self proves) Learn it, and learn it well. Long term it will bring you nothing but good.

    No 'topping off' ffs. Recover charge. Fix leak. Pressure leak test. Vac out. Recharge.
    If you have not the skills and/or tools to do this get a profesional in. < That advice is a damned good start!

    Do it right and you'll be hareld as a hero! Do it wrong and the court jester will out rank you!

  18. #18
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: mixing 404 wit 502

    Do you wear your "spurs" when working on equipment?

Similar Threads

  1. Oil mixing problem - Help needed !
    By Rio69 in forum Technical Discussions
    Replies: 11
    Last Post: 26-02-2008, 05:36 AM
  2. Chilled water system
    By Rabindra in forum Air Conditioning
    Replies: 6
    Last Post: 23-10-2007, 08:06 AM
  3. re heater
    By Coolie in forum Technical Discussions
    Replies: 17
    Last Post: 21-11-2004, 10:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •