ammonia transfer
Hello Sirs,..
how are you all....?
due to environment not allowed , I have question, anybody experienced for transfer the ammonia gas from evaporative condenser system to ammonia filled tank?
If have experience please kindly share to me how to do?
many thanks and waiting for the advise.
-
29-02-2008, 03:29 AM #2
Re: ammonia transfer
Hi Faryuki!
If I understand correctly, you want to know how to move the Nh3 from the system into a cylinder or other storage tank?
-
29-02-2008, 03:51 AM #3
Re: ammonia transfer
Yes Sir , that is move into the cylinder
many thanks
-
29-02-2008, 04:27 AM #4
Re: ammonia transfer
You can use an ammonia transfer unit much like on a large chiller. It consist of a small piston type compressor, a condenser, and a receiver to store the refrigerant. You can use a push-pull to get any liquid out first. Put the suction on the storage receiver and discharge into the condenser to push out any liquid to the storage receiver. Then take suction from the condenser and put the condensed liquid into the storage receiver.
In the US, there are a number of companies that rent the "pump out units" or will provide the service. You might check with your ammonia supplier.
Ken
-
29-02-2008, 06:02 AM #5
Re: ammonia transfer
By far the bast way to do this is with a pump out machine. If it is not available we can discuss other methods. Please describe your system and exactly what you need to do. Are you shutting the system down?
-
29-02-2008, 04:24 PM #6
Re: ammonia transfer
get the professionals you need a special operators licence
-
03-03-2008, 10:33 AM #7
Re: ammonia transfer
Thanks before.
I have three big evacon for chiller and have problem with the pipe, all pipes in and out are corroded and we have to replace all. each evacon have service valve in and out and we do one by one evacon for replacement pipe. and i have to removed ammonia inside of evacon and store into ammonia cylinder.
its possible???
kindly need yours advice.
many thanks
-
04-03-2008, 12:24 PM #8
Re: ammonia transfer
If you want to empty one condensor at a time and have isolating valves upstream of area that needs relaceing ,can you isolate it leaving plant running ?
Assuming you have a valve to atmosphere you can use a pressure rated hose to transfer it to a lower preesure area in system or in suction of commpressor downstream of its suction service valve.
Then throttle suction service valve open line from condensor you want to empty.You would most likely have to lower or bridge out low pressure control to achieve a slight vacuum in this line/condensor.
If you put a gauge on valve or line you are pumping out you can monitor it as you go,as it may take several goes.Make sure you can unload commpressor during this process
-
19-03-2008, 03:32 AM #9
Re: ammonia transfer
many thanks for the advice...
bye
-
19-03-2008, 08:01 PM #10
-
27-03-2008, 02:27 AM #11
Similar Threads
-
Want to be trained as an ammonia operator
By Randy Williams in forum NH3Replies: 7Last Post: 26-11-2008, 08:15 PM -
Releasing ammonia into the environment.
By Tycho in forum NH3Replies: 21Last Post: 03-02-2008, 05:10 PM -
Ammonia and CO2 reactor
By gwapa in forum NH3Replies: 18Last Post: 07-01-2007, 04:50 PM -
Ammonia Transfer System
By gwapa in forum FundamentalsReplies: 7Last Post: 12-09-2006, 01:12 PM -
New Ammonia Certification in United States
By JerrydNH3 in forum NH3Replies: 11Last Post: 15-08-2006, 03:10 PM