    cascade system



    Hi,all
    Who can tell me how to operate a cascade system?
    High stage is R22.Low stage is R23.
    charging refrigerants?
    special cases to be attention during operation?
    .....
    Of course it is best there is a correlative manual . I'm a greener to this system.



  2. #2
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: cascade system

    First thing to do is to get the high temp stage down to temperature. Charge in a conventional manner for the R-22.

    You will need to vacuum dehydrate both systems to a fairly dry state and break the vacuum with the appropriate refrigerant.

    Hope fully the R23 system is design properly with an expansion tank or a fade-out drum. It should be a critical charge system.

    With the high temp system operating, charge vapor into the R23 side of the cascade condenser until you can get a liquid seal on the low temp system. Now start the low temp compressor and trim the charge as you are down to temperature.

    Ken

  3. #3
    Join Date
    Mar 2006
    Location
    China
    Posts
    86
    Rep Power
    19

    Re: cascade system

    Thanks,TXiceman.
    To avoid the air in R23 system,I wanna purge R23 through the low stage,about 2~3bar,is Ok?

  4. #4
    Join Date
    Jun 2007
    Location
    Norway
    Age
    74
    Posts
    56
    Rep Power
    17

    Smile Re: cascade system

    If this is a already made system, I would have looked for the spesifications on the unit. The high stage capacity and temperature should be correct at the start. Do not look for a "normal" pressure reading on it because a high stage without load can go into wild low pressures. Earlier days I was used to R12 on the high and it went to -45c so people without knowledge always filled the high up and made a new problem to another. The low stage in most cases use a static filling pressure by ambient which give you the best charge. Some other make a static after a run and in such systems, I normally charge +10% which drop down to correct on the new test after after test warming up. If you charge a low stage just by looking for an end temperature, you have to be careful so you not overcharge the system. You can get dangerous pressure when it warm up again.

    Have a nice weekend you all

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. R-23 cascade system
    By S.M.Gokhale in forum Industrial
    Replies: 22
    Last Post: 08-08-2009, 08:04 AM
  4. problem in Auto Refrigeration Cascade System
    By ernestlin in forum Trouble Shooting
    Replies: 17
    Last Post: 01-07-2009, 12:41 PM
  5. Replies: 3
    Last Post: 24-03-2007, 02:50 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •