    Fault code for a mitsubishi heavy



    Im looking for fault codes for a Mitsi Heavy FDC 2501HK XE2
    I have been told that the fault is E36 or E42 the person who took the call can't remember and im going to look at it tomorrow.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Fault code for a mitsubishi heavy

    E36 should be discharge temperature abnormality.
    E42 should be current (compressor currentabn.).

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fault code for a mitsubishi heavy

    Quote Originally Posted by marc5180 View Post
    Im looking for fault codes for a Mitsi Heavy FDC 2501HK XE2
    I have been told that the fault is E36 or E42 the person who took the call can't remember and im going to look at it tomorrow.
    E36= Compressor discharge temperature:
    • The discharge temperature is abnormally high
    • Insufficient refrigerant
    • Poor airflow through condenser coil
    • Compressor discharge temperature sensor (ThOD) defective

    E42= Compressor Current:
    • Abnormally high current detected in inverter compressor

    Good luck!

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault code for a mitsubishi heavy

    great stuff thankyou.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fault code for a mitsubishi heavy

    E 36
    "Discharge temperature abnormality"
    "A stop occurs when this abnormality occurs for 2 seconds running at 130°C.
    After a stop for 3 minutes, an recovery is automatically made.
    An abnormal stop occurs when this abnormality occurs 2 times for 60 minutes.
    (The abnormal state is held for 45 minutes.)"


    E42
    "Current cut" (translates to compressor over-current in proper English)
    "An abnormal stop occurs when this abnormality occurs 4 times for 15 minutes."

    The above is from the manual for the 280, but I assume the fault codes and descriptions are the same.


    (I need to learn how to touch type. But hey, at least we agree)

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault code for a mitsubishi heavy

    Update, dont know why i was told E42 or E36. I set off this morning at 3.30am got to westminster at 8am (bad traffic as usual) and on the main controller the fault code was E05 which meant indoor/outdoor transmission. so straight away i went to the outdoor board to find no power so the i checked the isolator to find it off. I spoke to the manager who said that E05 had been flashing up for the past 2 days.
    I stayed with it for a few hours to check that the isolator hadn't been turned off for a reason and the unit ran fine and didn't fault once.
    So 5 hours down there to turn on an isolator..... very frustrating
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fault code for a mitsubishi heavy

    But not always unusual for London or some other cities.

    Either vandals or people living in flats who can't sleep with the noise of the condensing unit running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault code for a mitsubishi heavy

    Funnily enough the condensors are on a locked roof inside the hotel and only 2 people have the key. Although any number of the hotel guest could literally climb out of their window and switch them off. But if that was the case then why only one? there are 5 of them.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  2. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  3. Mitsubishi SRK 40 HG Fault Code. Help Please.
    By smoking_muzzle in forum Air Conditioning
    Replies: 3
    Last Post: 11-07-2007, 05:30 PM
  4. fault codes for mitsubishi heavy industries air con
    By mal in forum Trouble Shooting
    Replies: 1
    Last Post: 21-10-2006, 06:20 PM
  5. Fault Code Sheets...?
    By C_Henderson in forum Air Conditioning
    Replies: 2
    Last Post: 01-08-2006, 05:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •