    onder



    Hi everyone !

    1)I need your help.Right now I have been buy a new booster Frick RWF II 856.What do you think about this model ? ( Advantages Disadvantages )
    2) do you have any experiences about desuperheater systems ?
    Regards,



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: onder

    Are you talking about desuperheaters for water or refrigerant (for low stage to high stage compressors)?
    If all else fails, ask for help.


  3. #3
    ondero's Avatar
    ondero Guest

    Re: onder

    I want to use Hp compressor discharge gas for water heating with phe

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: onder

    Make sure the PHE is able to drain the liquid refrigerant as it condenses in the heat exchanger. If liquid accumulates in the PHE because it cannot drain properly you will loose the heating capacity of the PHE.
    If all else fails, ask for help.


  5. #5
    Join Date
    Dec 2006
    Location
    turkey
    Age
    51
    Posts
    8
    Rep Power
    0

    Re: onder

    If you contact to frigo mekanik from turkey . be sure they will assist you .