    Re: chiller problems

    iceman,

    I think you have a serious flooding/slugging problem during the run cycle. Busted valves are obvious and a shorted motor can also be the result of a flooding condition. One important rule to remember is that a mechanical problems can cause an electrical failure.

    A common example is during floodback the crankcase fills with liquid refrigerant which is heavier than oil. The oil pump pickup tube picks up a oil/liquid refrigerant mixture. As this mixture is pumped through the crankshaft it lubricates somewhat but eventually boils off. The last bearing, which supports the rotor, wears out. The rotor then drops and drags on the stator............shorted windings.

    The 6RP2 is a refrigerant cooled compressor and hard to slug during the run cycle.........but not impossible.

    I would start with a hard look at the TEV and other controls.

    Also, adding a suction accumulator is good but, sometimes it's just a bandaid which cannot cure the problem.

    Good luck
    Last edited by powell; 27-02-2008 at 08:13 PM.

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  3. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Replies: 7
    Last Post: 13-08-2010, 08:12 PM
  4. problems with york yaa c chiller
    By paulwild in forum Commercial
    Replies: 4
    Last Post: 21-08-2007, 08:20 PM
  5. Chiller coldroom compressor problems.
    By Lucas in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2004, 11:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •