    Water Coolers



    Hallo to everybody !

    Please, I would be grateful if somebody could help me, since I didn't find a useful post about this issue:
    Premise:
    For condensers, you can specify the capacity in a certain condition.
    The capacity in a different condition can be, as a rule of thumb, be calculated with the variation of temperature between air and condensing temperature.
    This is the so called "heat rejection", that is expressed in kW/K.

    Please, it there a similar rule that can be applied for water coolers ?

    If not, do you know or do you utilize if there any rule to calculate the capacity of chillers in a condition different than a specified one ?

    Thanks in advance !



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Water Coolers

    I would think that a water cooler would operate in a reasonably stable environment.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2006
    Location
    italy
    Posts
    37
    Rep Power
    0

    Re: Water Coolers

    Hallo Mr. Brian,

    I am sorry, but I don't understand completely your question.
    My question is theoretical, of course I suppose the water cooler is operating in a stable condition.

    Maybe, apologizes for this, I am not been clear enough.
    What I mean is:
    I have a water cooler (the heat sink is the air).
    I have got the capacity in a certain condition.
    Is it possible to determine roughly the capacity in a condition different than the starting one starting form the given capacity ?

    Thanks and good night !!

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Water Coolers

    Quote Originally Posted by MrReds View Post
    Hallo Mr. Brian,

    I have a water cooler (the heat sink is the air).
    I have got the capacity in a certain condition.
    Is it possible to determine roughly the capacity in a condition different than the starting one starting form the given capacity ?

    Thanks and good night !!
    Roughly, maybe 6 to 10% loss for a 10 F increase in ambient, or 6 -10% gain for a 10 F decrease in the ambient temperature. The base design was probably around a 90 F ambient.

    These are SWAG numbers that should be close. If you need exact you should contact the manufacturer.

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  4. water cooled subcooler?
    By star882 in forum Technical Speculations
    Replies: 1
    Last Post: 29-12-2007, 11:21 PM
  5. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •