    407c Charge



    Hi guys.
    Need to recharge a system, but do not have a vapour charger 'from bottle to guage', bottle has both vapour and liqiud ports, is it o.k to charge from vapour port through suction service valve??

    Don't shoot me down if this is a stupid question.
    Cheers.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: 407c Charge

    No, it is not ok. Charge from liquid phase to avoid distillation of blend. Use the liquid port in suction valve, making sure that very little liquid is reaching the compressor.

  3. #3
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: 407c Charge

    Hey N.Lewis...best to charge in the liquid state.Pretty much the same reason as when charging a refrigeration system with R404A.So R407C and R404A are zeotropic refrigerants,which means they are blends.Hope this helps....

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 407c Charge

    What is size of system?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 407c Charge

    Charge in liquid state only.

    Throttle back on your manifold valve like a manual expansion valve if charging into a running compressor or until the vacuum has been broken.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: 407c Charge

    Thanks guy's, i knew it was a dumb question even as i was posting it, but had to make sure, oh well we all have blonde moments...

Similar Threads

  1. To charge or not to charge?
    By Fire and Ice in forum Old Refrigeration Photos
    Replies: 12
    Last Post: 20-01-2008, 08:11 PM
  2. low charge or cap tube blockage ?
    By NC joe in forum Trouble Shooting
    Replies: 8
    Last Post: 12-11-2007, 06:25 AM
  3. Help please. How to charge a unit
    By God55 in forum Air Conditioning
    Replies: 18
    Last Post: 23-03-2007, 10:07 AM
  4. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Replies: 4
    Last Post: 01-12-2006, 07:40 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •