26-02-2008, 06:10 PM #1
407c Charge
Hi guys.
Need to recharge a system, but do not have a vapour charger 'from bottle to guage', bottle has both vapour and liqiud ports, is it o.k to charge from vapour port through suction service valve??
Don't shoot me down if this is a stupid question.
Cheers.
-
26-02-2008, 06:30 PM #2
Re: 407c Charge
No, it is not ok. Charge from liquid phase to avoid distillation of blend. Use the liquid port in suction valve, making sure that very little liquid is reaching the compressor.
-
26-02-2008, 09:03 PM #3
Re: 407c Charge
Hey N.Lewis...best to charge in the liquid state.Pretty much the same reason as when charging a refrigeration system with R404A.So R407C and R404A are zeotropic refrigerants,which means they are blends.Hope this helps....
-
26-02-2008, 09:05 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 407c Charge
What is size of system?
-
26-02-2008, 09:17 PM #5
Re: 407c Charge
Charge in liquid state only.
Throttle back on your manifold valve like a manual expansion valve if charging into a running compressor or until the vacuum has been broken.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
27-02-2008, 09:21 AM #6
Re: 407c Charge
Thanks guy's, i knew it was a dumb question even as i was posting it, but had to make sure, oh well we all have blonde moments...
Similar Threads
-
To charge or not to charge?
By Fire and Ice in forum Old Refrigeration PhotosReplies: 12Last Post: 20-01-2008, 08:11 PM -
low charge or cap tube blockage ?
By NC joe in forum Trouble ShootingReplies: 8Last Post: 12-11-2007, 06:25 AM -
Help please. How to charge a unit
By God55 in forum Air ConditioningReplies: 18Last Post: 23-03-2007, 10:07 AM -
Subcooling vs charge graph?
By Larry2 in forum FundamentalsReplies: 4Last Post: 01-12-2006, 07:40 PM -
Who's in charge?
By chillin out in forum Chit Chat & Service StoriesReplies: 1Last Post: 01-10-2006, 10:51 PM