Thread: daikin no heat
    Feb 2008
    nicholasville kentucky
    daikin no heat
    i have a sky air one to one what happens in the heat mode, eveything come on, and for about 2 min i will get the ssupply air up to 94degf and the discharge line will also. and then that temp drops back down as if a valve closes the outdoor unit still runs and then cycles off with no fault.
    Split Croatia
    57
    6,151
    36
    Re: daikin no heat
    Maybe you need to clean filters!
    Apr 2007
    West Midlands
    45
    55
    Re: daikin no heat
    So are you saying the unit thinks it's achieved it's set temp and therefore shuts down as it should? If so maybe you have a faulty TH air on thermistor?
    Doe's it work ok on cooling, switch off on on with temp?
    Chris
    Apr 2001
    79
    5,071
    35
    Re: daikin no heat
    Check the outdoor airflow also. Is the coil frozen?... dirty?... fan running properly?
    Nov 2006
    Scotland
    43
    85
    Re: daikin no heat
    Best to do a proper system check,mate.Thats electrically and mechanically as well...
    11,025
    Re: daikin no heat
    Possibly a blocked filter in the outdoor unit.
    Feb 2008
    Re: daikin no heat
    i found that the reversing valve is sticking. took temp across to verify this. ordered new valve and going to replace