i have a sky air one to one what happens in the heat mode, eveything come on, and for about 2 min i will get the ssupply air up to 94degf and the discharge line will also. and then that temp drops back down as if a valve closes the outdoor unit still runs and then cycles off with no fault.
-
26-02-2008, 01:43 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: daikin no heat
Maybe you need to clean filters!
-
26-02-2008, 05:43 PM #3
Re: daikin no heat
Hi
So are you saying the unit thinks it's achieved it's set temp and therefore shuts down as it should? If so maybe you have a faulty TH air on thermistor?
Doe's it work ok on cooling, switch off on on with temp?
Chris
-
26-02-2008, 05:44 PM #4
Re: daikin no heat
Check the outdoor airflow also. Is the coil frozen?... dirty?... fan running properly?
-
26-02-2008, 09:17 PM #5
Re: daikin no heat
Best to do a proper system check,mate.Thats electrically and mechanically as well...
-
27-02-2008, 12:03 AM #6
Re: daikin no heat
Possibly a blocked filter in the outdoor unit.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
27-02-2008, 03:48 AM #7
Re: daikin no heat
i found that the reversing valve is sticking. took temp across to verify this. ordered new valve and going to replace
Similar Threads
-
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
heat exchanger for small chiller
By star882 in forum FundamentalsReplies: 4Last Post: 30-01-2007, 12:06 PM -
Daikin HP on heat mode
By Latte in forum Air ConditioningReplies: 10Last Post: 06-12-2005, 10:24 PM