    i have a sky air one to one what happens in the heat mode, eveything come on, and for about 2 min i will get the ssupply air up to 94degf and the discharge line will also. and then that temp drops back down as if a valve closes the outdoor unit still runs and then cycles off with no fault.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: daikin no heat

    Maybe you need to clean filters!

  3. #3
    Join Date
    Apr 2007
    Location
    West Midlands
    Age
    45
    Posts
    55
    Rep Power
    17

    Re: daikin no heat

    Hi
    So are you saying the unit thinks it's achieved it's set temp and therefore shuts down as it should? If so maybe you have a faulty TH air on thermistor?

    Doe's it work ok on cooling, switch off on on with temp?

    Chris

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: daikin no heat

    Check the outdoor airflow also. Is the coil frozen?... dirty?... fan running properly?

  5. #5
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: daikin no heat

    Best to do a proper system check,mate.Thats electrically and mechanically as well...

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daikin no heat

    Possibly a blocked filter in the outdoor unit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Feb 2008
    Location
    nicholasville kentucky
    Age
    46
    Posts
    6
    Rep Power
    0

    Re: daikin no heat

    i found that the reversing valve is sticking. took temp across to verify this. ordered new valve and going to replace

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. heat exchanger for small chiller
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 30-01-2007, 12:06 PM
  5. Daikin HP on heat mode
    By Latte in forum Air Conditioning
    Replies: 10
    Last Post: 06-12-2005, 10:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •