    Cool Water flowcalc
    I have the pipe dia and the water flow in l/s. Hoe do I measure the actual flow with only a pressure guage
    Re: Water flowcalc
    You need an orifice to enable you to measure a pressure differential.
    Aug 2007
    SOUTH AFRICA
    8
    Re: Water flowcalc
    How does one convert l/s into kpa. We have the pipe dia in mm
    Feb 2007
    2,473
    Re: Water flowcalc
    Quote Originally Posted by chan View Post
    Well, you don't...
    To be able to measure the flow by observing pressure, you need to measure pressure difference across a known resistance in the pipework.
    For example; across an orifice or a plate heat exchanger.
    Aug 2007
    SOUTH AFRICA
    8
    Re: Water flowcalc
    OK so how does one determin that the flow rate in a system is as it is designed. What is the correct instrument that should be used?
    Feb 2007
    2,473
    Re: Water flowcalc
    KPA is a measure of pressure.
    l/s is a measure of flow......
    Under certain given condition there will be a relationship between them.
    Therefore you would have to put one in to a formula to calculate the other.
    (That formula will depend on measuring device used)
    But you will not be able to "convert" one to the other.
    Croatia
    68
    2,261
    Re: Water flowcalc
    Hi, chan
    water flow meter
    Best regards, Josip
    Feb 2007
    2,473
    Re: Water flowcalc
    Click on THIS link.
    That document shows a balancing valve with built in measuring point.
    After that has been installed, you would measure the pressure drop between the 2 ports (pointing down from the valve body in the colour picture).The Red port would read a slightly higher pressure than the Blue one.
    Then you would be able to find out the flow by checking the pressure drop against a graph supplied by the valve manufacturer.
    (THIS is the type of pressure meter you would require for the job.)
    But there are other ways of measuring water flows, as Jossip says, use a water flow meter. These could be piped in, ultrasonic, magnetic and so on.
    Jun 2005
    Romania
    213
    Re: Water flowcalc
    whell to be more streghit, to messure a flow u need a pressure diff, and a pipe diamenther, because withe one pressure gage u only have one pressure, so the system might be on a hight presure on a low pressure, depending and the building hight, and pressure loss on the fan coil, or whatever u have.
    So ... by nessuring the the difference u reduce the problem to one pressure, and u get the formula for how muth whater flow do u get for that dyamenther on that pressure.
    And that's the closest u get to what a flow mether calculates
    Croatia
    68
    2,261
    Re: Water flowcalc
    Hi, chan
    ....., I read your post again .... you have your flow, why you need pressure
    ....can you explain a little more problem you have, maybe
    Best regards, Josip
    Re: Water flowcalc
    I wonder if he means that he has the design flow rate ?
    Feb 2008
    Sussex UK
    54
    Re: Water flowcalc
    To mearsure the flow correctly you need to know the design pressure drop and measure the actual drop with a pressure gauge or perflow meter, in a binder point near the point you are measuring.. on and off..
    So i.e. if you have the design pressure drop divide this by the actual pressure drop you read, then square root it..times this by the design flow rate this will then give you the actual flow rate in l/s..but remember the temp diff you are looking for, this will have an effect on the flow rate. So not as easy as just reading a flow rate....
    Jan 2008
    Norfolk - England
    95
    Re: Water flowcalc
    Hi Viking,
    thats looks like a nice flow meter!
    Are they accurate & do you know how much they cost?
    Billy Ray
    Feb 2007
    2,473
    Re: Water flowcalc
    Quote Originally Posted by Billy Ray View Post
    Hi Viking,
    Billy Ray
    Accurate, YES
    Cost...An arm and a leg and then some, we normally rent them.
    But if you contact BSRIA they will be able to quote you. (www.bsria.co.uk)
    wdrzal's Avatar
    wdrzal Guest
    Re: Water flowcalc
    A mass flow meter is used to measure pressure differantial across a orfice or a pressure differantial.It requires 2 access points and a thermocouple for temperature. Mine has a pressure accuracy of .02 psi.
    Or you can use a non-invasive Doppler/ultrasound to measure the flow rate inside the pipe/tube. The hand held one I have has a sensor that straps to the pipe,it runs on 45 volt (5 - 9v batteries). The doppler shift picks up any bubbles or turbulance to give a reading in feet per second.Then by using a simple formula you can calulate the flow.
    Aug 2005
    5,302
    Re: Water flowcalc
    If using a flow meter you need to ensure the instrument is not connected right after an elbow or control valve also. These introduce inaccuracies that can lead to incorrect readings.
    Jan 2008
    Norfolk - England
    95
    Re: Water flowcalc
    Thanks Viking,
    Billy ray
  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Last Post: 09-03-2009, 06:19 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Last Post: 09-11-2008, 06:37 PM
  4. water cooled subcooler?
    By star882 in forum Technical Speculations
    Last Post: 29-12-2007, 11:21 PM
  5. open cycle R718 A/C that also provides high purity water?
    Last Post: 27-07-2006, 04:18 AM