    Hot Gas Bypass



    Hi Guys,

    I would like to know the % of HOT GAS that can be bypassed into the evaporator?

    Also, I have a scenario where TX valve was not completely open and when HG was bypassed, the suction pressure didn't change.

    I'll appreciate the comments.

    Regards.



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Hot Gas Bypass

    Quote Originally Posted by jwasir View Post
    Hi Guys,

    I would like to know the % of HOT GAS that can be bypassed into the evaporator?
    jwasir,

    Here's a couple links to Sporlans technical forms explaining hot gas bypass. They will give you a good understanding of how a HGB valve works and how they are designed for a particular application.

    Powell

    Design literature: http://www.parker.com/literature/Lit...0090/90-40.pdf

    Operation and service: http://www.parker.com/literature/Lit...0090/90-41.pdf

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Hot Gas Bypass

    Typically the percentage of hot gas required is determined by the minimum step of compressor capacity if the compressor has capacity control increments,

    or,

    if the compressor has no capacity reduction then the hot gas would be sized for the percentage of load reduction you expect to see from the evaporator. Let's say the evaporator load has the probability of reducing to 50%. To keep the compressor operating satisfactorily the hot gas valve would be sized for 50%.

    or,

    you can use a variable frequency drive down to the minimum speed allowed by the compressor manufacturer.
    If all else fails, ask for help.


  4. #4
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Hot Gas Bypass

    To suppliment US Iceman, On air conditioning systems, the minimum allowable evaporating temperature that will avoid coil icing depends on evaporator design and the amount of air passing over the coil. The refrigerant temperature may be below 32°F, but coil icing will not usually occurwith high air velocities since the external surface temperature of the tube will be above 32°F. For most air conditioning systems the minimum evaporating temperature is 20°F to 25°F. However, when air velocities are reduced considerably, the minimum evaporating temperature should be 26°F to 28°F.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Hot Gas Bypass

    Quote Originally Posted by wambat
    However, when air velocities are reduced considerably, the minimum evaporating temperature should be 26°F to 28°F.
    I have seen this on refrigeration coils also. The return bends and deaders tend to frost up but the coil & fins stay relatively clean where uniform air flow exist.
    If all else fails, ask for help.


  6. #6
    rcschebler's Avatar
    rcschebler Guest

    Re: Hot Gas Bypass

    The standard for % of hit gas bypass is no more than 50% of the compressors capacity. As far as your TX problem, the suction pressure should have gone up when the bypass valve modulated open. The addition of hot gas would increase superheat, causing the TXV to open to compensate. Check you TXV powerhead. Good luck.

  7. #7
    sailer's Avatar
    sailer Guest

    Re: Hot Gas Bypass

    Is this sys chill water cooled, too much cooling and the coil pressure drops that can cause the HGB to be unable to control .
    What is the application?
    Is the HGB adjusting it self or starting from a closed
    position. On some systems you should not be
    able to detect a pressure change with out digital gauges,{ if you can the unit is unstable}and the HGB should be replaced. Give the guys more info

  8. #8
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Hot Gas Bypass

    Quote Originally Posted by rcschebler View Post
    The standard for % of hit gas bypass is no more than 50% of the compressors capacity. As far as your TX problem, the suction pressure should have gone up when the bypass valve modulated open. The addition of hot gas would increase superheat, causing the TXV to open to compensate. Check you TXV powerhead. Good luck.
    If i not mistaken the standard for % of hit gas bypass is no more than 40% of the compressors capacity.
    In some places will have to think ...

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Hot Gas Bypass

    I really dislike hot gas defrost system, should be re-named cool gas defrost and the evaporator then becomes a condenser and fires great slugs of liquid back to the plant room and low side accumulator.

  10. #10
    Join Date
    Sep 2007
    Location
    philippines
    Posts
    8
    Rep Power
    0

    Re: Hot Gas Bypass

    on a standard procedure or operation how can i know if the hot gas bypass is operating. thank you.

  11. #11
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    19

    Re: Hot Gas Bypass

    Quote Originally Posted by Brutus View Post
    on a standard procedure or operation how can i know if the hot gas bypass is operating. thank you.

    Grab the HG line, it will be warmer/ hot!
    Check the solenoid, if energised!

Similar Threads

  1. Scroll internal bypass
    By Larry2 in forum Heat Pumps
    Replies: 27
    Last Post: 15-05-2009, 09:23 AM
  2. old system with hot gas bypass. help!
    By joapysoe in forum Trouble Shooting
    Replies: 8
    Last Post: 20-01-2008, 11:58 PM
  3. Dont be shy, advice needed.
    By Sledge in forum Air Conditioning
    Replies: 9
    Last Post: 27-06-2007, 03:09 PM
  4. Hot gas bypass control?
    By Jase in forum Air Conditioning
    Replies: 9
    Last Post: 29-10-2006, 11:21 AM