    Hello my first post
    Anyone have any advice on detecting a leak on 3 pipe VRV sytem over 3 floors high with approx. 20 cassette units attached to it.
    Tried UV dye and the usual soap solution
    going out of my head trying to locate this leak
    my next step is to split the piping into three parts. Seal the ends and pressure test each on seperately hoping to find it.
    Anyone got any advice
    jacob odeyemi's Avatar
    jacob odeyemi Guest
    Re: Leak tracing
    have you tried any of the leak detectors around? either electronic or ultrasound i think they are handy enough and will save you a lot of time and stress from jacob
    11,025
    Re: Leak tracing
    Are you leak checking with the refrigerant present or are you using high pressure OFN ?
    Jan 2008
    Manchester, Uk
    57
    Thumbs up Re: Leak tracing
    If you know there is a leak somewhere on the system, then you will need to recover and weigh all the refrigerant. The chances are the system will be short of its correct charge anyway, so by recovering the refrigerant you will be able to calculate how much you need to put back in. Whilst the refrigerant is out of the system, you will be able to carry out a high pressure leak test which will find your leak(s). Once you've repaired the leak(s), you can carry out another pressure test (and strength test) to be sure you've no more, before evacuating and re-charging. Trust me- it'll save you time in the long term. Andy C.
    May 2001
    North Wales
    47
    Re: Leak tracing
    d-tek IR leak tester. Damn Grill thing, well recommended, already paid for its self. Only had it short while!
    Apr 2007
    West Midlands
    45
    55
    Re: Leak tracing
    just curious,
    When you guys leak test with OFN how much "trace" refrigerant do you leave in the system to use your electronic leak detector, i was always told and therefore left 10 psi in.
    By rights all should be removed i know but near every engineer i know does this - even the best.
    (talking large systems really)
    Chris
    11,025
    Re: Leak tracing
    Gives you a lot of contaminated OFN to deal with at the end though doesn't it ?
    11,025
    Re: Leak tracing
    Hey M4X1MU5
    are you still out there ?
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: Leak tracing
    Hi Chris
    I read in a book that the ASHRAE guide lines say 15 psi r22 is acceptable for trace then topped up with dry nitro
    Apr 2007
    West Midlands
    45
    55
    Re: Leak tracing
    Is that only for R22 then, what about 407c, thought it was ozone friendly compared to R22?
    Chris.
    M4X1MU5's Avatar
    M4X1MU5 Guest
    Re: Leak tracing
    Yeah Guys Thanks A Whole Heap
    I ended Up Spliting The Runs And Pressure Testing With OFN Found The Leak
    The Previous Contractors Had Condemned A BS Box And Didn't Seal THe Piping Propely and Had A Hairline Crack.
    THe Situation was not helped by the entire cieling being in plaster board. Ended up having the entire ceiling being cut open everywhere.
    Again thnx guys
    11,025
    Re: Leak tracing
    Glad to hear that you have found your problem and thanks for the update.
    Did you get them to build in a proper access panel for future use?
    Split Croatia
    57
    6,151
    36
    Re: Leak tracing
    That is what aggravates me most with interior architects. Their lack of cooperation on placing acess panels is more and more frustrating.
    Again, I still exult when I need to open plasterboard to reach some component of system.
  1. Leak detectors
    By Temprite in forum Tools and Calculators
    Last Post: 18-08-2010, 04:15 PM
  2. Evasive gas leak
    By Feeze in forum Technical Discussions
    Last Post: 18-08-2008, 07:22 AM
  3. Help!!! Shell and Tube Evap Leak
    By tommy Gun in forum Trouble Shooting
    Last Post: 22-07-2007, 12:45 PM
  4. Tiff 5000 leak detector
    By davidchesson in forum Tools and Calculators
    Last Post: 06-11-2006, 04:26 AM
  5. Can't find leak with UV Dye
    By jd_boggs in forum Transport
    Last Post: 16-09-2006, 06:22 PM