    Daikin



    Hi,
    I'm working on a daikin VRV2 heat recovery tomorrow (not sure of the model number) which is faulting on an "E4"
    fault but as i hardly ever work on these units i can't remember how to be sure all the solonoids and expansion valves are open when pressure testing and vaccing out.

    Can anyone point me in the right direction on this one please?


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin

    E4 can also be faulty sensor or pcb im trying to email you manual for this unit to your e mail in your v card it is quite alrge file so not sure if it will work if you dont get the file call daikin on 01932879200 and they will talk you thriugh the open all valves procedure the down side is you have to leave the power on to the unit whilst testing which isn't ideal

  3. #3
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Daikin

    Hi Marc
    It's Manual No SiE39-306 you want off the Extranet.

    Someone correct this if it's wrong..

    Recovery Mode-
    Press & Hold MODE till H1P is Lit Solid
    Press SET 21 times until LED's are-
    ON OFF ON OFF ON OFF ON
    Press RETURN Once- H7P flashing
    Press SET once- H6P flashing
    Press RETURN Twice

    Hope this helps

    Ginge

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin

    then return to exit after u have finished driving the valves open.

  5. #5
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin

    Quote Originally Posted by Gingerair View Post
    Hi Marc
    It's Manual No SiE39-306 you want off the Extranet.

    Someone correct this if it's wrong..

    Recovery Mode-
    Press & Hold MODE till H1P is Lit Solid
    Press SET 21 times until LED's are-
    ON OFF ON OFF ON OFF ON
    Press RETURN Once- H7P flashing
    Press SET once- H6P flashing
    Press RETURN Twice

    Hope this helps

    Ginge
    Spot on

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    That's great guys, thanks.

    Why don't Daikin make it simple like Mitsi?

    Also thanks for the email james10, that will come in handy tomorrow for sure.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin

    Quote Originally Posted by install monkey View Post
    then return to exit after u have finished driving the valves open.
    then press MODE to exit after u have finished driving the valves open (to close valves again when finished)
    Or switching mains on/off will also have same result

  8. #8
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: Daikin

    hey guys do any of you posses the manual for the pcb modes etc, i phoned daikin but they failed to send me one would much appreciate if some one could send one via e-mail. You can download my Vcard
    Last edited by frank; 21-01-2011 at 12:57 PM.

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    The units in question is a reyq10m8w1b x2

    Got to site this morning, unit running with no fault codes yet air off on heating 28C.

    Checked fault history and found unit 0 "JC" fault but no "e4" fault which had been reported.

    Does anyone have the manual for this one that shows error codes? I'm unable to log onto extranet whilst at work using my PDA.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin

    Jc=Malfunction suction pipe sensor/defect low pressure sensorsystem/connection high pressure with wrong connection/defect outdoor pcb board
    Daikin text service 07797801908 just text the fault code to that number and they text you straight back with error description i'll email you error code list all daikin codes are the same regardless of system type

  11. #11
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    Thanks, traced the problem to a low pressure transducer that was faulty.
    All sorted now.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  12. #12
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin

    Quote Originally Posted by marc5180 View Post
    Thanks, traced the problem to a low pressure transducer that was faulty.
    All sorted now.
    better than having to find a leak on the buggers

  13. #13
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin

    hi marc if its the low pressure transducer can that be changed without removal of refrigerant?

    cheers lee

  14. #14
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Daikin

    I can't believe a man of you calibre hasn't got a daikin service checker...

  15. #15
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    Quote Originally Posted by moondawn View Post
    hi marc if its the low pressure transducer can that be changed without removal of refrigerant?

    cheers lee
    Im not too sure Lee, i've looked in the manual but it doesn't say anything about removal of LP sensor.

    I'm hoping i don't have to remove the refrigerant maybe someone on here will know
    The difference between genius and stupidity is that genius has its limits.

    Marc

  16. #16
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    Quote Originally Posted by Gingerair View Post
    I can't believe a man of you calibre hasn't got a daikin service checker...
    It's taken me 4 years to get hold of the Mitsubishi monitoring tool and i work on that kit all the time.

    We don't do much work on Daikin VRV's which is why i haven't really pushed to get one but it could all change so it may be worth investing in one.

    How easy is it to get the service checker and is there a course to go on to show you how to use it?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  17. #17
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Daikin

    Quote Originally Posted by marc5180 View Post
    Im not too sure Lee, i've looked in the manual but it doesn't say anything about removal of LP sensor.

    I'm hoping i don't have to remove the refrigerant maybe someone on here will know
    You can pump the system down Daikin calls this the adding refrigerant function or if you have more than one condenser shut the faulty units valves and recover the refrigerant into the other condensers easier and quicker than reclaiming the full charge

  18. #18
    Join Date
    Jan 2010
    Location
    Coventry
    Age
    36
    Posts
    37
    Rep Power
    0

    Re: Daikin

    The tranducers are on shrader valves anyway I had to change the discharge one on one of these units last month!

  19. #19
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Daikin

    The service checker isn't as hard to get hold of as the mitsi monitor tool, think as long as you're willing to cough up the cash they're happy to supply. Have been told recently that they do provide a course but not checked for sure. Think they may have recently published some more training course dates..

    I thought it was the older 407c type units that were the last to have schrader connections..

    If you've not got another condenser on the system you made need to recover the full charge, the only access valves for recovery, pressure testing/vaccing are on the main condensing unit isolation valves. You couldn't even close these & recover into the pipework cause there's no other access fittings on the condenser..

    I prefer Mitsi..

    Ginge
    Last edited by Gingerair; 23-01-2011 at 08:51 PM. Reason: Chicken or Beef ??

  20. #20
    Join Date
    Jan 2010
    Location
    Coventry
    Age
    36
    Posts
    37
    Rep Power
    0

    Re: Daikin

    Ohh could be actually it was an Rseyp I was working on 407c

  21. #21
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Daikin

    Daikin told me it's something to do with F-Gas why they changed, pain in the @ss if you ask me...

    P.S. Marc the manual No. for the Heat Pump model is SiE39-302
    Last edited by Gingerair; 23-01-2011 at 08:38 PM. Reason: Lemon Moose Cake...mmmmm....

  22. #22
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin

    Quote Originally Posted by moondawn View Post
    hi marc if its the low pressure transducer can that be changed without removal of refrigerant?

    cheers lee
    The pressure transducers on VRVII (M series) are connected using mushroom type schrader valves and can be replaced without removing gas charge.
    The transducers on VRVIII (P series) are weld in.

    Quote Originally Posted by Gingerair View Post
    Daikin told me it's something to do with F-Gas why they changed, pain in the @ss if you ask me...

    P.S. Marc the manual No. for the Heat Pump model is SiE39-302
    RXYQ- -M7&M8 VRVII heat pump manual - SiE39-302
    RXYQ- -M9 VRVII heat pump manual - Si39-407A

    RXYQ- -P7 VRVIII heat pump manual - Si34-601A
    RXYQ- -P8&P9 VRVIII heat pump manual - Si34-803A
    Last edited by VRVIII; 23-01-2011 at 09:10 PM.

  23. #23
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Daikin

    Handy info, thanks VRVIII

  24. #24
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin

    hi there going to fit this pressure transducer tomorrow, the system has 2 condensors both the same model number :reyq10m8w1b
    To stop the unit from going in to fault marc has used the mode buttons on the outdoor main board to disable the faulty condensor from the system therfore allowing it to run whitout faulting on the indoor remote controllers.

    Could someone please post how we are able to put the system back to how it was originally please.

    cheers lee

  25. #25
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    Ring Daikin, they don't bite
    The difference between genius and stupidity is that genius has its limits.

    Marc

  26. #26
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin

    OR..........
    Reset the power supply during the outdoor unit is stopping to cancel the
    automatic backup operation forcibly.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  27. #27
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin

    nothing wrong with being prepared marc, daikin are very busy people.

  28. #28
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin

    hi all fitted lp transducer system back up and running now. the transducer was a mushroom type shreader connection and simply unscrew it and replace with lp transducer.

    thanks all

    cheers lee

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  3. Daikin FDYQ250M
    By carl in forum Air Conditioning
    Replies: 7
    Last Post: 11-08-2009, 12:56 AM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •