Results 1 to 21 of 21
19-02-2008, 02:04 AM #1
Energy savings in Industrial Refrigeration
Here is an article some of you may find interesting if you are working on energy savings for industrial refrigeration systems.
http://www.hpac.com/Issue/Article/24472/24472If all else fails, ask for help.
19-02-2008, 02:42 AM #2
Re: Energy savings in Industrial Refrigeration
Iceman,
I'm glad you sent this article. Floating heads (Reduced Compression TM) can be very tricky. Every facility is different and this article is good. (although way to much info for free).
I have a chicken processing plant with ice and storage that I designed and rerofit that runs SDT as low as 40F.
On another plant I acually run my heads lower than some of the common suctions. Then when the heads are low enough I thermosyphon the load right to the condersers... Anyways good article. A little tricky...
Core4 Guy
19-02-2008, 03:02 AM #3
Originally Posted by Core4 Guy
Yes, these can be tricky but... it's just good engineering applied to real world conditions. What a thought, heh?If all else fails, ask for help.
19-02-2008, 04:18 AM #4
Hi, Mike.
I'd like to discuss one sentence from your article. "Minimum (head)pressure may be determined by operator preference...."?
Several years ago I read manual from one PLC manufacturer. I remember one sentence from this manual. "Every experienced operator with basic refrigeration knowledge can set up(tune up) this PLC"??? I was really shocked.
What is the goal in energy saving process? The goal to operate the refrigeration plant at optimum set points and at optimum operating strategies. Determination and implementation of these set points and strategies is the most important part of energy savings. Without these points and strategies every PLC is almost useless. Why every experienced operator should tune up the plant?
19-02-2008, 05:46 AM #5
Hi Sergei,
Then, you see someone selling control systems as manna from heaven promising all sorts of wonderful things. I think your example of the PLC was one of those. I would be shocked too. There is certainly more to a system operation than setting several control points.
The sentence you question was directed to those facilities where they think the minimum discharge pressure is what they have been operating at. When you see systems running with 180 psig discharge in the winter and you ask, why? The usual answer is the system needs to run at this pressure to operate properly. So, the situation becomes one of operator preference. It's what they think they need versus what the system capability actually is.
Perhaps...but it might be required because the system was designed so poorly. Even on a conventionally designed system you can get to 125 psig discharge with little problems. Less is certainly possible, but it does create issues when you try to convince people that it is possible.
After all, if it is a good idea... the system would have been designed to operate like that!If all else fails, ask for help.
19-02-2008, 05:53 AM #6
What is a "discharge HA backpressure valve"? That's a new term I have not heard before.If all else fails, ask for help.
19-02-2008, 03:58 AM #7
Iceman,
Compressor manufactures have to be queasy. Imagine if everyone tried this! There are alot of issues to overcome. We hold the warrenties on the compressors we use, just so manufactures will sell us compressors.
As far as the halocarbon industry I'm using carlyle and wanting to use turbocor machines. I find with a carlyle if don't exceed the mass flow rate of the machine and they will last. I have carlyles running with a 15# differentials with discharge HA backpressure valves holding back to allow me to lower my cond temp below suction for compressor free cooling. I call this MTS Cooling (TM) Modified Thermosyphon Cooling. It's not that easy but its worth it to have a compressor free load for 3600 hours a year in CA.
21-02-2008, 06:04 AM #8
Iceman, your right again. I'm kind of found of Hussmans Cool Gas Defrost too. It's all about latent heat. You know, I haven't thought this much in years. Thanks.
21-02-2008, 07:57 PM #9
Originally Posted by Core4 GuyIf all else fails, ask for help.
05-03-2008, 05:05 AM #10
I have found that my system operates well at condensing pressure as low as 100 psi, with no problems during hot gas defrosts. I have operated the system during cold weather and low heat load conditions with condensing pressure as low as 90 degrees without problems, but it just didn't "feel right" to me. Every system and every operator are different, and there are a gazillion variables in heat loads, but for me a pressure near 100 psi is just perfect.....
05-03-2008, 08:35 AM #11
Thanks man, I was looking for this
05-03-2008, 05:39 PM #12
Originally Posted by Oregon Jim
As you say, each system is different and some operators get really excited when you mention these concepts. It just takes some time and innovation to get something new accomplished.If all else fails, ask for help.
06-03-2008, 03:36 AM #13
My main concern with operating at low condensing temperature is due to worry about oil foaming within the compressors. I have an old Frick rotary booster compressor that is very prone to oil foaming and oil loss when the oil temperature gets too low. Of course foaming is not such a problem in my second stage compressors due to increased pressure, but because I am not an expert in oil behavior I become a tad nervous when my compressor temps begin to drop below their "normal" parameters.
As you said, adapting to change is difficult sometimes...