    It's a coincidence. In air-conditioning, the horsepower rating of the compressors approximates the tonnage. In refrigeration, the relationship does not exist. It causes a lot of confusion when people who are used to air conditioning step into the realm of refrigeration and refer to "tons" of refrigeration.
    Even "horsepower" as we use it only approximates horsepower, for that matter.
    St. Louis, MO
    510
    If we are simply converting units of power, we have:
    1 ton refrigeration = 4.712 horsepower, electric
    But when we try to relate compressor horsepower to tons refrigeration, we are not simply converting units. The work of the compressor is being used to move energy for the most part, and not change it as you would have with a resistance heater.
    So if we have a 16 EER a/c unit, which is to say we get 16 Btu/hr cooling for every watt of power used, and we note another conversion:
    1 watt = 3.412 Btu/hr
    We see that our 16 EER a/c unit is providing 16 / 3.412 = 4.69 watts of cooling for every watt of power used. This is also referred to as the coefficient of performance (COP).
    Some confuse this issue as getting something out of nothing, but this is hardly the case. Again, we are moving energy around, not converting it.
    So we get the following relationship with our 16 EER unit:
    1 hp, electric = 4.69 / 4.712 = 0.995 tons refrigeration
    Thus the one horsepower to one ton relationship with a/c units.
    As we try to achieve lower evaporator temperatures with refrigeration systems, more power is required to move the same Btus, and we require more horsepower to achieve a ton of cooling.
    Prof Sporlan
    Feb 2001
    Tampa Florida
    1,086
    Good post, Professor. It reminds me that horsepower and amperage may have a relationship. Permit me to use the word "draw" if I may.
    I recall seeing compressor curve charts where a 10 hp compressor and a 20 hp compressor have the same amperage draw under certain conditions. Is this possible?
    Apr 2001
    Question
    ok,so how do we determine the horsepower of a compressor in refrigeration,as it is not on the nameplate? ( besides phoning the supplier)
    Feb 2001
    Tampa Florida
    1,086
    Professor, your observation regarding the coincidence between the horsepower and tonnage thingy, was the first thing that came to my mind, when I observed the thread title....
    Jeesh. I never get credit for anything. It was I who used the word "coincidence." The Professor merely began to address the issue properly.
    Feb 2001
    Tampa Florida
    1,086
    Amperage. Amperage describes work. Voltage describes power.
    Like blow and suck. Voltage blows and amperage sucks, for example.
    There are are many ways to determine the horsepower of a compressor that has no nameplate. But a motor with no load and the same motor overloaded has a different horsepower.
    Nominal horsepower is what we are addressing. Nominal means "in name only."
    Horsepower and tons are probably some terms we need to abandon. Especially since we do not use melting ice for refrigeration and horses to deliver it. Clip clop.
    Apr 2001
    I seem to remember 1 hp = 746 watts...If we convert that to btu/h can't we determine tonnage? It doesn't seem to add up!!!
    St. Louis, MO
    510
    Compressor horsepower, of course, is simply a nominal rating point, no different than say a "10 ton" TEV.
    Actual TEV capacity will vary from its nominal rating, depending on the operating conditions. We could have a situation where a 10 ton and 20 ton TEV have the same rating, if appropriate operating conditions are selected for each.
    One would not expect a 10 and 20 hp compressor to be drawing the same amps at the same voltage if both were operating at the same conditions. But perhaps we could have a situation where they might operate very similarly if, say, the 20 hp compressor had a more efficient motor, and both compressors were operating at low suction pressures, near or outside their design envelope, with the 10 hp compressor delivering greater capacity per horsepower.
    Prof Sporlan
    St. Louis, MO
    510
    This is correct
    You need to account for the system's COP. See the Prof's example with the 16 EER a/c unit.
    Prof Sporlan
  1. Horsepower to tons/ref. conversion ?
    By Hank Hill in forum Tools and Calculators
    Last Post: 15-05-2010, 07:42 PM
  2. Large tonnage De-coupling
    By MANIS in forum Technical Discussions
    Last Post: 14-08-2004, 06:29 PM
  3. Horsepower and Kilowatts
    By baker in forum Air Conditioning
    Last Post: 23-03-2004, 09:17 AM