    Should suction accumulators be insulated?



    I always find excessive frosting on suction accumulators a nuisance. Any suggestion as to what are the causes and if insulation is the way to prevent it.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Should suction accumulators be insulated?

    It shows that the accumulator is doing the job it was designed for.

    Possible causes are liquid boiling off inside or perhaps due to the pressure drop through the accumulator causing the temperature change. It could also be due to low ambient temperatures.

    If you insulate it then you may loose the heating effect that is required for it to work properly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Should suction accumulators be insulated?

    Suction accumulators will frost if the refrigerant temperature is low enough, this is not necessaraly a problem (except excessive rusting).

    Suction accumulators are installed to collect refrigerant that has splashed over from the evaporator, typically in plants which have varying loads, blast chilling / process cooling etc. This is due to the ex valve not being able to control at the varying load conditions.

    My thoughts are that heat is required to evaporate the refrigerant collected, therfore a heat source is required.

    This could be achieved by leaving the accumulator uninsulated, however i prefer to use a accumulaor with the liquid line passing through. There is plenty of heat in liquid refrigerant avaialble, & a bonus of subcooling the liquid is achieved.

    Back to basics, you dont really want the ex valve hunting & causing the effect in the first place!!

    Billy Ray

  4. #4
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Should suction accumulators be insulated?

    If rust isnt a problem, yes. There is no ned for external heat for the trapped refrigerant to leave the accumulator. It is a smal hole in the bottom of the outlet tube. Trapped refrigerant (and oil) enters the outlet tube trough that hole. If that hole wasnt there the accumulator would be an absolutely terific oil accumulator or more precise an oil trap. The oil cant evaporate and wouldnt stand any chance in hell to escape the accumulator after first entering it.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Should suction accumulators be insulated?

    Quote Originally Posted by Billy Ray View Post

    This could be achieved by leaving the accumulator uninsulated, however i prefer to use a accumulaor with the liquid line passing through. There is plenty of heat in liquid refrigerant avaialble, & a bonus of subcooling the liquid is achieved.


    Billy Ray
    Here you talking about Combination Accumulator/Sub-Cooler !!

    http://tinyurl.com/2yav3c

  6. #6
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Should suction accumulators be insulated?

    Quote Originally Posted by Brian_UK View Post
    It shows that the accumulator is doing the job it was designed for.

    Possible causes are liquid boiling off inside or perhaps due to the pressure drop through the accumulator causing the temperature change. It could also be due to low ambient temperatures.

    If you insulate it then you may loose the heating effect that is required for it to work properly.
    I agree.


    But, if the frost is persistent or semi permanent, then rust may deteriorate the surface metal of the accumulator as was already pointed out - it is, after all, a pressure vessel and must be safe at all times and protected from corrosion.

    Presuming that there are no problems with the system that is causing liquid to settle back through the suction line, vapour that is below the dew point will always attract moisture from the air.

    However, if insulation is unavoidable, (for example the ice is presenting a hazard), Why not consider a small heater with insulation?
    A crankcase heater, a hundred Watts or so, depending on the size of the vessel, and some insulation may solve the problem.

    Heat in the accumulator you want - ice on the outside you don't.


    .

  7. #7
    superheated's Avatar
    superheated Guest

    Re: Should suction accumulators be insulated?

    thanks all, great help.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Should suction accumulators be insulated?

    I replaced an accumilator last year and insulated it as the original had been insulated. I believe it was a Henry accumilator, which was the same diameter as a model of that companies oil seperators, so i got a heater for an oil seperator and fitted that too as the original also had a heater.

    Jon

Similar Threads

  1. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. suction line freezeing
    By karimihassan in forum Air Conditioning
    Replies: 4
    Last Post: 05-08-2007, 05:17 AM
  4. Suction Accumulators
    By rsiyer in forum Technical Speculations
    Replies: 2
    Last Post: 15-06-2007, 04:16 AM
  5. Replies: 10
    Last Post: 18-03-2006, 07:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •