Results 1 to 16 of 16
Thread: R404A charge
    Jan 2008
    China
    73
    R404A charge
    R404A must liquid charge.
    1) How to liquid charge ?
    2) How to know the charge is OK ?
    Split Croatia
    6,106
    7
    30
    Re: R404A charge
    Quote Originally Posted by Ding Kangzhi View Post
    1. Depends of refrigerant drum type. If it is without tube to the bottom (inside) then you need to turn it upside down. If it is with tube, then in normal position.
    Check with sight glass in service manometer that is full with liquid. If you have liquid accumulator charge it in accumulator first and then top up on suction side carefully and with throttling (quick charger or with valve)
    2. Charge by weight if it is known. If not, then charge by subcooling and superheat. Simulate low ambient conditions and ensure enough superheat and soubcooling.
    Read this:
    http://www.mediafire.com/?3xggwmbndxx
    Sep 2006
    Indonesia
    5
    Re: R404A charge
    Hi Ding Kangzhi,
    Better you add one port access for charging and one handvalve on the liquid line, if you want to charge the system while shutdown, just charge in to the port access.
    after you start the system and found that the liquid line sight glass has not full yet, so you close the hand valve and top up from the port while the pressure at that side lower than your refrigerant cylinder.
    Make sure what is the working pressure that you use.
    best regards,
    Martua
    Jan 2008
    China
    73
    Re: R404A charge
    I am informed that when charging R404A, the compressor can not shutdown, must running the compressor and using sight glass method to charge.
    Can you tell me more about charge the sytem while shutdown ? Thanks
    crazykev's Avatar
    crazykev Guest
    Re: R404A charge
    shutdown ? Thanks
    Use only this method ,while shutdown is when your commissioning a new system or your lost the entire gas charge ...and your evacuated the system.While in vacuum & charge to full sightglass.
    Overwise , if its screw compressor just put your 60 kg bottle on the suction & let it go.
    Recip compressor , you need tread with alittle more caution & watch your discharge temperature ..Plus
    too much liquid refrigerant in your sump with an oil pump .You would lose your compressor on oil pressure switch.
    I have re -top up 400 kilo systems ,this method on 404a.
    Jul 2007
    Australia
    44
    1,857
    14
    Re: R404A charge
    does it have a liquid reciever and sightglass?
    Or is a a critcal charge system, ie no liquid reciever?
    Jan 2008
    China
    73
    Re: R404A charge
    There are sightglass and water cooled condensor in system.
    Dec 2006
    Philippines
    38
    Re: R404A charge
    Is it a new installed cold room???
    Jun 2005
    U.K.
    Re: R404A charge
    can anyone tell me what does a pp fault mean on a carel control
    Split Croatia
    6,106
    7
    30
    Re: R404A charge
    Quote Originally Posted by saud khan View Post
    What Carel model are you referring to?
    Jan 2008
    China
    73
    Re: R404A charge
    Quote Originally Posted by Philip View Post
    It is both new installed and repair after leakage
    dr_ace_2008's Avatar
    dr_ace_2008 Guest
    Re: R404A charge
    Quote Originally Posted by Achiel_refri View Post
    Hi Ding Kangzhi,
    best regards,
    Martua
    hallo boss martua ??
    where is your position now??
    iran,,singapore,,or batam
    are yoy still in viking
    sorry if i'm knowing the wrong guy,,
    ady simamora
    riddhisiddhi's Avatar
    riddhisiddhi Guest
    Re: R404A charge
    hi,
    pp means probe fail (temp sensor) of controller
    Greajh's Avatar
    Greajh Guest
    Re: R404A charge
    Im working in hospital we have Nuaire-86'c freezer with 2 stage compressor.Do you have any idea on how to charge R404,R134A/R508,R134A are they mixed up when charging pls help me?
    thanks and more power,
    44
    3,798
    38
    Re: R404A charge
    Quote Originally Posted by Greajh View Post
    Try contacting the manufacturers, they should be able to help with you with information.
    Dec 2010
    devon
    47
    784
    Re: R404A charge
    you have a cascade system one refrigerant isthe others condensor start with the lest efficient refrigerant and work up these refrigerants are not mixed they are seperate do not mix at any cost all ref should be labelled on machine and watch the very low temp ref they can have high head pressure
  1. To charge or not to charge?
    By Fire and Ice in forum Old Refrigeration Photos
    Last Post: 20-01-2008, 08:11 PM
  2. Why not R404a?
    By afak in forum Technical Speculations
    Last Post: 02-04-2007, 08:58 PM
  3. Help please. How to charge a unit
    By God55 in forum Air Conditioning
    Last Post: 23-03-2007, 10:07 AM
  4. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Last Post: 01-12-2006, 07:40 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Last Post: 01-10-2006, 10:51 PM