    Re: sensible cooling duty of a cooler

    Hi US iceman,

    not so sure here in europe!!

    Most manufacturers i understand test to eurovent conditions (set out by europe commissionin). These conditions i believe are for 'wet' coils i.e sensible & latent cooling.

    Generally i have been told that on stated nominal conditions 80% sensible / 20% latent will be in the order.

    I may well be misinformed & hopefully a cooler manufacturer will correct me.

    Billy Ray

  2. #2
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: sensible cooling duty of a cooler

    further more......

    its a bit of an open ender..

    if you select your compressor based on the cooler at 100% sensible, & if, which is most likely that latent cooling will be performed (due to room conditions)...

    The compressor will be undersized..

    Billy Ray

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: sensible cooling duty of a cooler

    For air conditioning coils I would agree with you. I think the AC cooling coil capacities are based on a specific sensible heat ratio.

    However, for refrigeration coils "they" are listed as sensible only cooling. Then, if you have a coil which operates below freezing the defrost correction factors increase the required coil capacity to account for the time off in defrost.

    But please bear in mind I am speaking from my background here in the US.

    This is one of those subjects where it pays dividends to read the fine print. The literature should say what the cooling capacities are based.

    Our methods may be different than yours.
    If all else fails, ask for help.


  4. #4
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: sensible cooling duty of a cooler

    totally agree with you, 'read the fine print' because you dont always get what you think your getting!!

Similar Threads

  1. cooling tower's free cooling issue
    By Lc_shi in forum New Technologies
    Replies: 12
    Last Post: 30-01-2011, 04:41 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Replies: 13
    Last Post: 08-02-2002, 11:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •