    Feb 2008
    Georgia
    64
    capillary tube clogs
    Can anyone tell me what causes cap tube clogging besides debris? The problem seems restricted to POE oil and R134a. Is there a prevention?
    3,856
    Re: capillary tube clogs
    I remember reading about something called 'metal soap' caused by a chemical reaction within the system.
    Jan 2008
    Kent UK
    49
    514
    Hi.I read somewhere that this is a common problem with R134a and they found it was due to dirty condensers and high head pressures.As for a prevention i can only suggest keeping condensers clean. http://www.patentstorm.us/patents/59...scription.html
    Last edited by Brian_UK; 14-02-2008 at 12:20 AM. Reason: adding url Changed font size to a more readable one.
    3,856
    This mentions metal soap
    Its also mentioned a bitzer report
    Cheers Jon
    Feb 2008
    Las Vegas, NV
    67
    330
    Quote Originally Posted by hotrodluvr View Post
    The number one problem would be heat. Prevention would be to keep the system clean.
    If you had a leak and there wasn't a LPC then moisture could also enter the system which along with the heat produced would break down the oil.
    Aug 2007
    Sydney
    52
    1,083
    23
    Yes Chunky Monkey
    I agree - high head temps are the cause of this even with r22. It forms a coke like black substance in the wall of tube. maintenance and clean condensers is the cure.
    Oct 2005
    nottingham UK
    109
    when 134a was first being used in bottle coolers and small fridges we had lots of them blocking, when we sliced open the cappilary we found a white wax type of restriction which would if left off long enough allow flow again until cabinet reached temp and would then again block.always ended up witha new evap complete with cappillary.
  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Last Post: 16-11-2010, 11:44 PM