    capillary tube clogs



    Can anyone tell me what causes cap tube clogging besides debris? The problem seems restricted to POE oil and R134a. Is there a prevention?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: capillary tube clogs

    I remember reading about something called 'metal soap' caused by a chemical reaction within the system.

  3. #3
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: capillary tube clogs

    Hi.I read somewhere that this is a common problem with R134a and they found it was due to dirty condensers and high head pressures.As for a prevention i can only suggest keeping condensers clean. http://www.patentstorm.us/patents/59...scription.html
    Last edited by Brian_UK; 14-02-2008 at 12:20 AM. Reason: adding url Changed font size to a more readable one.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: capillary tube clogs

    This mentions metal soap

    http://www.patentstorm.us/patents/59...scription.html

    Its also mentioned a bitzer report

    Cheers Jon

  5. #5
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: capillary tube clogs

    Quote Originally Posted by hotrodluvr View Post
    Can anyone tell me what causes cap tube clogging besides debris? The problem seems restricted to POE oil and R134a. Is there a prevention?
    The number one problem would be heat. Prevention would be to keep the system clean.

    If you had a leak and there wasn't a LPC then moisture could also enter the system which along with the heat produced would break down the oil.

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: capillary tube clogs

    Yes Chunky Monkey
    I agree - high head temps are the cause of this even with r22. It forms a coke like black substance in the wall of tube. maintenance and clean condensers is the cure.

  7. #7
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: capillary tube clogs

    when 134a was first being used in bottle coolers and small fridges we had lots of them blocking, when we sliced open the cappilary we found a white wax type of restriction which would if left off long enough allow flow again until cabinet reached temp and would then again block.always ended up witha new evap complete with cappillary.

Similar Threads

  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Replies: 7
    Last Post: 16-11-2010, 11:44 PM
  2. Distributor & Capillary tube position
    By MrReds in forum Technical Discussions
    Replies: 12
    Last Post: 29-03-2008, 07:40 AM
  3. Capillary tube prices in the UK
    By trial in forum Fundamentals
    Replies: 4
    Last Post: 18-09-2007, 12:16 PM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •