    Re: Mitsubishi ecodan Heatpump Boiler



    Quote Originally Posted by brunstar View Post
    Daikin Altherma have released a high temperature range which operates to temperatures of up to 80 degrees.
    The perfect solution for UK climates which most tech's will be able to work on which is a great solution by the looks of it.
    I would love to know what compressor model these are using.

    At a water delivery temp of 80'C, SCT must be >=~80'C, unless pulling a little more from the refrigerant superheat. Even then SCT must be at least 75'C.

    Wonder what lifetime testing these folks have to back up their claims. I'd be intrigued.



    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #52
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Mitsubishi ecodan Heatpump Boiler

    I'm thinking the more relevant question would be, how do they regulate/limit the heat generated by the compressor motor?

  3. #53
    Join Date
    Mar 2006
    Location
    timbuktu !
    Posts
    24
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    Anything that operates above the trans-critical stage is not going to be good for COP in order to produce 65 to 80 degrees C,granted it will have its market for retro fits which will have marginal efficiency benefits against gas/oil.

    We must harness the way we heat our domestic dwellings - low temperatures that the 'normal' energy cycle provides with condensing temps of 40-50 degrees C is the main way forward.

  4. #54
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by Gary View Post
    I'm thinking the more relevant question would be, how do they regulate/limit the heat generated by the compressor motor?
    Yes, agreed.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #55
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by desA View Post
    I would love to know what compressor model these are using.

    At a water delivery temp of 80'C, SCT must be >=~80'C, unless pulling a little more from the refrigerant superheat. Even then SCT must be at least 75'C.

    Wonder what lifetime testing these folks have to back up their claims. I'd be intrigued.

    From what little I have found online, it seems that Daikin builds their own compressors and if I am not mistaken, the Altherma uses an inverter driven model.

  6. #56
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Mitsubishi ecodan Heatpump Boiler

    ^ Thanks very much, Gary. I'll follow up on their compressor range.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #57
    Heatman's Avatar
    Heatman Guest

    Re: Mitsubishi ecodan Heatpump Boiler

    I've been looking at the Daikin HT heat pump any one know what SCOP figures. I've been told likely to be around 2, which seems low. Can't get any actual performance details from Daikin, anyone got any experience?

  8. #58
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by Heatman View Post
    I've been looking at the Daikin HT heat pump any one know what SCOP figures. I've been told likely to be around 2, which seems low. Can't get any actual performance details from Daikin, anyone got any experience?
    If you e mail technicalhelp@daikin.co.uk with the heading of Daikin Altherma HT information and the nature of the query they will be able to help you.

  9. #59
    Join Date
    Mar 2006
    Location
    timbuktu !
    Posts
    24
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by Heatman View Post
    I've been looking at the Daikin HT heat pump any one know what SCOP figures. I've been told likely to be around 2, which seems low. Can't get any actual performance details from Daikin, anyone got any experience?
    more likely your not able to supply them with the correct criteria in order to give you an exact SCoP...hence im guessing the figure was quoted by them as worst case scenario.(THEY HAVE SOME VERY GOOD SOFTWARE SO IT IS EASY FOR THEM)

    This figure is realistic at worst case up to around 2.5.

    And yes you are correct for traditional cycle its not the best, but it does use two compressors utilising R410a & R134a gas as a cascade type system to boost to 80 degrees C.

    Although the COP does not on the face of it seem that good, the product is MCS approved unlike alot of those out there that arent, and dont forget the government is now going to PAY people for every kwh they use from an ASHP up to around 7p per KWH up to 23 years of the systems life (dont shoot me if its 6p!)

    Hence with the £900 grant plus the above - makes it the most cost effective solution now well above boilers !

    hope this helps.

  10. #60
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    24
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by krychek View Post
    .................. and dont forget the government is now going to PAY people for every kwh they use from an ASHP up to around 7p per KWH up to 23 years of the systems life (dont shoot me if its 6p!).........
    from Krycheks profile :

    Location: timbuktu !


  11. #61
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Mitsubishi ecodan Heatpump Boiler

    The high temperature units have quite a good COP compared to CO2 units. By the use of 2 compressors it does sound like a lot more energy but if you plot the compression cycle due to the cascade system the heat of compression is lower bringing the discharge pressure and temperature closer to that what a CO2 system will offer which increases the refrigeration effect making the system more efficient.(lower your head pressure and system becomes more efficient). The COP will only depend on what flow temperature you are running the system at!

    Just like all of the low temperature systems out there the COP is calculated at 35 degree flow most of the time but people run the system at higher flow temperatures than required reducing the COP and wasting energy.
    Daikin UK have a cash back scheme on their Daikin Altherma High temperature units and Daikin Altherma Monobloc units which is extremely attractive!!!
    check this out, up to 1800 pounds cash back..

    http://www.altherma.co.uk/500-cash-back/default.jsp

  12. #62
    Join Date
    Mar 2006
    Location
    timbuktu !
    Posts
    24
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by olddog View Post
    from Krycheks profile :

    Location: timbuktu !

    lol - not a bad place to be....!!

  13. #63
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by krychek View Post
    and dont forget the government is now going to PAY people for every kwh they use from an ASHP up to around 7p per KWH up to 23 years of the systems life (dont shoot me if its 6p!)
    This is mentioned in a consultation document going through Parliament at the moment.....far off being accepted, which is just as well, as the proposal is to slap a levy on all our energy bills to pay for it.

    Search for the document on line....the front page is attached below
    Attached Images Attached Images

  14. #64
    Join Date
    Aug 2008
    Location
    uk
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    Hi, very interesting thread this, keep it up. My ex-council house is fitted with the regulation baxi back boiler and i've been weighing up my options for a while, my understanding is that mitsi and daikin both have high temp versions, my only worry is that a cascade ashp means two compressors and more parts to fail etc, i wonder how this affects the long term return
    also does anyone know how much these things cost GBP ?? that's assuming i can get 'em to sell me one

  15. #65
    Join Date
    Jan 2011
    Location
    scotland
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    Hi there we have experienced the same problems could you PM me please
    Last edited by frank; 26-01-2011 at 08:04 PM.

  16. #66
    Join Date
    Jan 2011
    Location
    scotland
    Age
    50
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi ecodan Heatpump Boiler

    do your self a favour stay away from mitsubishi when it comes to air sourse heat pumps PM me and I will explain why
    Last edited by frank; 26-01-2011 at 08:05 PM.

  17. #67
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    58
    Posts
    724
    Rep Power
    22

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by sweeney948 View Post
    do your self a favour stay away from mitsubishi when it comes to air sourse heat pumps PM me and I will explain why

    Please tell us here, we'd like to know..
    Last edited by frank; 26-01-2011 at 08:06 PM.
    Karl

  18. #68
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    58
    Posts
    724
    Rep Power
    22

    Re: Mitsubishi ecodan Heatpump Boiler

    Quote Originally Posted by Haden4ever View Post
    Hi, very interesting thread this, keep it up. My ex-council house is fitted with the regulation baxi back boiler and i've been weighing up my options for a while, my understanding is that mitsi and daikin both have high temp versions, my only worry is that a cascade ashp means two compressors and more parts to fail etc, i wonder how this affects the long term return
    also does anyone know how much these things cost GBP ?? that's assuming i can get 'em to sell me one
    I would say that your best option would be to stick with gas for an older property onless you were planning to gut the house and fit underfloor and upgrade the insulation considerably
    Karl

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Mitsubishi vrv
    By dakesojo in forum Air Conditioning
    Replies: 20
    Last Post: 22-09-2009, 01:04 PM
  2. Replies: 6
    Last Post: 12-12-2007, 12:38 AM
  3. Mitsubishi Light Truck Refrigeration
    By Mastercool in forum Transport
    Replies: 2
    Last Post: 23-11-2007, 07:15 AM
  4. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 11:23 PM
  5. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •