    Problems with Air Source Heat Pump



    Hi ,
    Ive a recent problem with Air Source Heat Pump in Heat Mode.
    With Outside Air Temp at 1deg C the Outdoor unit pipework at the Outdoor Unit measures 58degC & 18 Deg C. and at the Input of the Indoor Unit the Pipework its 55 & 20 Deg C.
    However I must of knocked the pipework a few weeks back & had a very slight leak on one of the fittings... I've nipped this up & checked everything tight with soapy water.. However temperatures inside are struggling to get above 20 degC & noticed that the outside evaporator only ices up at the bottom 1/3 & no higher( however i don't know if this is normal)... Would this be due to loss of coolant because pipe temperatures do seem pretty good I would think.. At 6dec C outside air temp yesterday the pipes at the Outdoor unit in Heat mode where 64deg C & 21Deg C respectively measured with a digital thermocouple.. Any help would be appreciated



  2. #2
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Problems with Air Source Heat Pump

    Quote Originally Posted by brizy View Post
    Hi ,
    Ive a recent problem with Air Source Heat Pump in Heat Mode.
    With Outside Air Temp at 1deg C the Outdoor unit pipework at the Outdoor Unit measures 58degC & 18 Deg C. and at the Input of the Indoor Unit the Pipework its 55 & 20 Deg C.
    However I must of knocked the pipework a few weeks back & had a very slight leak on one of the fittings... I've nipped this up & checked everything tight with soapy water.. However temperatures inside are struggling to get above 20 degC & noticed that the outside evaporator only ices up at the bottom 1/3 & no higher( however i don't know if this is normal)... Would this be due to loss of coolant because pipe temperatures do seem pretty good I would think.. At 6dec C outside air temp yesterday the pipes at the Outdoor unit in Heat mode where 64deg C & 21Deg C respectively measured with a digital thermocouple.. Any help would be appreciated
    Thats some serious DT's you're getting there. Where are you taking your measurements?
    Is this an air to water unit?
    What type of heat distribution system have you?

  3. #3
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Problems with Air Source Heat Pump

    It would seem you have answered your own question in that you've lost some refrigerant charge with your 'leak' which will result in loss of duty.

    BTW Soapy water is not a good thing to use as a leak detector on refrigeration pipework.

    I'd sugest you contact a contractor to check your charge and pipework integrity.


    Which manufacturer is it?
    He who dies with the most Toys, WINS!

  4. #4
    brizy's Avatar
    brizy Guest

    Re: Problems with Air Source Heat Pump

    Its a 12K BTU Unit Bergdorf, Use to heat my shed during winter, temperature reading taken with a digital thermocouple with the probe touching pipework 1. At the Outdoor Unit Couplings & 2 at the Indoor Unit Couplings

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problems with Air Source Heat Pump

    I take it this is an air to air heat pump, in which case the high temp pipe in heat mode would be the discharge line.

    The increase in discharge line temp would seem to indicate an increase in superheat, which would indicate a shortage of refrigerant. Partial frosting of the outdoor coil would tend to confirm this.

  6. #6
    brizy's Avatar
    brizy Guest

    Re: Problems with Air Source Heat Pump

    Cheers Gary, thanks for the help with this...Looks like an engineer call out if thats the case... Anyone a rough guestimate looking at the Outdoor Unit ratings its 1080g of R410a thats required

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problems with Air Source Heat Pump

    Quote Originally Posted by brizy View Post
    Cheers Gary, thanks for the help with this...Looks like an engineer call out if thats the case... Anyone a rough guestimate looking at the Outdoor Unit ratings its 1080g of R410a thats required
    If I were the engineer repairing your system, I would undo and redo your leak repair, recover and evacuate the system and charge with fresh refrigerant. Only then could I guarantee the repair.

  8. #8
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Problems with Air Source Heat Pump

    Tis the only way forward OP!
    He who dies with the most Toys, WINS!

Similar Threads

  1. Problems with LG split heat pump M/N LS902hpv
    By joshbloomberg in forum Heat Pumps
    Replies: 5
    Last Post: 08-12-2010, 05:10 PM
  2. Air to air Source Heat Pump DIY Design Help
    By jones_d56 in forum Fundamentals
    Replies: 6
    Last Post: 14-10-2010, 07:51 PM
  3. Addition of a heat pump to solar heating system
    By rt29781 in forum Heat Pumps
    Replies: 24
    Last Post: 23-01-2010, 08:46 AM
  4. Homemade Heat Pump...
    By AC_Hacker in forum New to RE
    Replies: 0
    Last Post: 29-04-2009, 11:30 PM
  5. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Replies: 2
    Last Post: 10-02-2003, 01:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •