Results 1 to 8 of 8
Thread: discharge pressure too high
Hybrid View
13-02-2008, 06:39 PM #1
hello everybody...
i'm new in refrigeration so i want to know why the discharge pressure is to high even if i run only 1 compressor.the pressure is 50 psi suction & 225 psi discharge,if i run 2 compressor,suction pressure is the same value but discharge will go higher to 300 psi.can you help me...
13-02-2008, 07:54 PM #2
Re: discharge pressure too high
First,
We do need more information about your system to be able to assist you....
Secondly,
To me, 300 PSI head pressure sounds absolutely normal but this will depend on the refrigerant used and what system we are looking at.
13-02-2008, 07:59 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Please, tel us saturation temperatures instead of pressure, also subcooling and superheat. Then, air or water temperatures in and out of evaporator and condenser.
13-02-2008, 11:54 PM #4
14-02-2008, 07:25 AM #5
High head press is not caused by the compressor if thats any help. Check charge, evap load and firstly the condenser, then expansion valve
14-02-2008, 02:09 PM #6
thank you,i will check my chiller as you just mention.
16-02-2008, 05:21 PM #7
First you need to convert head pressure to saturated condensing temperature (SCT) using a pressure temperature (P/T) chart. Then you need to determine the temperature of the air entering the condenser. The difference between these two temperatures (condenser TD) should be 20-35F/11-19.5K. If the TD is in this range, then the pressure is normal.
16-02-2008, 08:58 PM #8
Hey buddy,looks like you getting answers from all over here.Follow the advice given,but do efficiency tests on the compresors just to be sure,they are the heart of the system after all.Then just take it from there....hope it helps...
Benji