    Calculate cap tube



    Any tool (online) available to calculate cap tube size/lenght for specific application.

    I've got my 100' roll of BC-1 on it's way for the -40F+ R-409A 100w video card chiller application on its way, but I'd rather not have to cut the dern tube down fourteen times before I am happy with it.

    :\



  2. #2
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    I called SUPCO, they couldn't help me. I need to determine cap tube length (preferrably for .031" cap tube I.D.) for approx. 250BTUH @-40F R-409A.


  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    How long is the cap tube on the Prommie?

  4. #4
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    How long is the cap tube on the Prommie?
    I'd guess about 48". The actual suction line is about 3' total length, and the way it's wrapped it......


    47" of .031" cap tube (according to the SUPCO info) is applicable to a 1/4 HP LBP (-10 SST). SUPCO couldn't give me any recommendations fo <-40.

    I asked the guy if he had the equations to determine the cap tube length required. He said that the guy that had those equations retired.... and took 'em with him!!!!!

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I wonder if Chipcon (mfg of prommie) would be willing to share that info?

  6. #6
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Are you going to call them?..... or should I?


  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Which of us is getting paid for this job?

  8. #8
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Originally posted by Gary
    Which of us is getting paid for this job?
    Well, 'ought dern it! I don't feel like calling Denmark.


    I think I'll start with 60" of .031.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    There's a new thing called "email".

    http://www.chip-con.com/index.php?pageid=35

    I think I'll start with 60" of .031.
    I was thinking 120". Easier to cut than to add.

  10. #10
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    I think cap tubes are a guess and bygosh arrangement.

    Lol. To some extent, Dan, you are correct. But there has been decent tables set up over the years which make it relatively simple for the design engineer to zero in on a proper capillary tube sizing. Also, the Prof has noted some interesting papers published in recent years describing refrigerant flow thru capillary tubes, so there are still some people studying the subject.
    Posted by the prof in March of 2001. LOL.

    Perhaps the prof would share one of these tables with Herefishy! Recently I posted in another discussion that the subject was discussed in the Fridgetech pages, but it wasn't there. Who would think to search this site? Now all I have to do is recall what that discussion was so I can search the Refrigeration-Engineer website. I bet that's where it lies!

    On a lighter note, when you dig up a discussion 2 years ago and see Gary's picture. He was holding the same grandchild. Maybe it is not so much a bitch getting old.

  11. #11
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    The Prof suspects that there hasn't been extensive study on cap tube sizing for the R-12 service replacement refrigerants... other than charge the system till is works right...

    When he gets back to the office, he'll look up low temp R-12 cap tube sizing in his Harry Busby reference, and see if it provides a suggested cap tube size.
    Prof Sporlan

  12. #12
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    thanks, Prof. It is a real honor to have you get off the bench for me. LOL!!!!

    Yeh, Gary.... after thinking about it some more... I was thinkin' about starting at 10' too! (we must be phsychotic)

    Particularly since I'm welding one end of this cap tube into a small copper block.... I don't want to be doing and undoing that connection..


    see ya'


  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    I've just been looking up cap tube sizing in one of my reference books and came across some info under "Expansion Devices". The calcs are quite prolonged and complicated to post but the book is by McGraw-Hill - Refrigeration & Air Conditioning (ISBN 0-07-061619-1).

    It also states that there are some selection charts in the Ashrae Manual - can't seem to find my Ashrae CD so I can't verify this

    Frank

  14. #14
    Join Date
    May 2002
    Location
    The Netherlands
    Age
    48
    Posts
    274
    Rep Power
    22
    I do have a few scanned pages from the ASHRAE handbook, with a few covering captube sizing. I won't post them here in public, but I am willing to share them through E-mail.

  15. #15
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Hi DaBit,

    Since you mentioned it, I just pulled my ASHRAE handbook off the shelf, and found the information you reference. I am reviewing it now.

    Thanx

  16. #16
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    The Busby reference suggests 12 ft of 0.031" capillary for an R-12 low temp (-10°F evaporator) system using a 1/6 hp compressor. Doesn't provide a Btu/hr rating, though.

    It also suggests 12 ft of 0.026" capillary for an R-12 low temp 1/12 hp compressor, which probably better matches your application.

    The reference doesn't give a conversion from 0.026" capillary to 0.031", but the Prof would estimate 24 ft of 0.031" capillary would be equivalent to 12 ft of 0.026".

    The 2002 ASHRAE Refrigeration Handbook provides capillary tube capacities for R-134a and R-410A.

    R-409A at 100°F liquid and -40°F evap will have a net refrigerating effect of about 55.5 Btu/lb. For a 250 Btu/hr load, we will need 250 / 55.5 = 4.5 lb/hr flow rate thru the capillary.

    According the the ASHRAE Handbook, R-134a at 150 psi liquid line pressure, zero subcooling, and 130" of 0.034" capillary will give us a 9 lb/hr flow rate. And according to ASHRAE, 200" of 0.030" capillary will give us a correction factor of 0.65, giving us 9 * .65 = 5.85 lb/hr.

    Mmmm... this should put us in the ballpark...
    Prof Sporlan

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I've found sizing tables at this site under technical infomation, but I think we will need an interpreter, as it's written in metric technospeak. I have enough problems trying to figure out SI technospeak.

    Perhaps Prof could explain it to us.

    http://www.cubigel.com/english/frprod.htm
    Last edited by Gary; 04-06-2003 at 02:00 AM.

  18. #18
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Most excellent, Professor.

    I had determined a required flow rate of approximately 5 lbs./hr.

    In conversation with the dude at Supco, we figured an equivalent of 1/8hp (for cap tube purposes) capacity out of the 1/4 horse compressor @-50F.

    In reviewing the chart for Pressure-Drop for Capillary Liquid, If I reference the 5LB PER HOUR line, and hit the .031 ID department, the indicated pressure drop per foot = 3.0

    If I assume a condensing pressure of about 170 R-409a, and a suction of 10"Hg vaccum (-5 psig?), at 175 psi pressure drop, I would require 58 feet?

    __________________________________________________

    I went through an example in the book.

    I determined:

    flow rate = 5lb/hr
    absolute inlet pressure = 175psia
    mass flow rate from a chart 38 = 72lb/hr
    flow factor (5/72) = .07

    and using this information, referencing a chart 39 (the book was saying reference chart 42... but that was an error) I come up with about 375" of .031.

    ...or 31.25' of .031" I.D. cap tube...

    if we change the enthalpy to the prof. suggested 55.5 btu/lb and the 4.5 req'd lbs/hr that changes the flow factor to .06.... that would make the cap tube longer (4.5/72).

    hmmmmm. 24'..... or ...... 31'
    Last edited by herefishy; 03-06-2003 at 05:07 PM.

  19. #19
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    In reviewing the chart for Pressure-Drop for Capillary Liquid, If I reference the 5LB PER HOUR line, and hit the .031 ID department, the indicated pressure drop per foot = 3.0
    What chart might this be? If this chart estimates pressure drop for liquid flow only, it would underestimate pressure drop for a capillary tube used as the expansion device, as it will see two-phase flow somewhere along its length.

    If I assume a condensing pressure of about 170 R-409a, and a suction of 10"Hg vaccum (-5 psig?), at 175 psi pressure drop, I would require 58 feet?
    In the Prof's humble opinion, 58 ft won't be necessary here...

    and using this information, referencing a chart 39 (the book was saying reference chart 42... but that was an error) I come up with about 375" of .031.

    ...or 31.25' of .031" I.D. cap tube...
    Not too far from the Prof's guesstimate...

    hmmmmm. 24'..... or ...... 31'
    It will always be easier to shorten the capillary...

    Perhaps Prof could explain it to us.
    The ASHRAE Refrigeration Handbook has a rather complicated eight term correlation to predict capillary tube flow rate... It includes the refrigerant's vapor and liquid specific volume, vapor and liquid viscosity, surface tension, specific heat, among other variables. This model apparently have been found to work well with R-22, R-134a, and R-410A. Other than the surface tension variable, the Prof has an Excel spreadsheet capable of generating the necessary thermodynamic data for this correlation. Mmmmm.... But it would hardly be appropriate for the Prof to be developing a cap tube selection program..
    Prof Sporlan

  20. #20
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Originally posted by Prof Sporlan
    What chart might this be? If this chart estimates pressure drop for liquid flow only, it would underestimate pressure drop for a capillary tube used as the expansion device, as it will see two-phase flow somewhere along its length.

    The chart to which I refer Fig 43 of section E19.29 of my....1988.... Ashrae handbook (equipment). Whose title is "Pressure-Drop Chart for Capillary Liquid (R-12 and 22)".

    on the "x" axis is Mass flow - lbs per hour, and the "y" axis indicates pressure drop per foot - psi. The linear relationship of the cap tube size if charted for .20" to .020" I.D.

    And now, if I look at it closer, a more accurate estimation of the reference point would be more like 1.5 psi per foot.

    so 175psia pressure drop would be more like 262.5". or 21.875'

    I think I'll start with 24' of .031. I have a 100' roll, and I seem to have two or three sources, now that point to around the 24' department.

  21. #21
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    The chart to which I refer Fig 43 of section E19.29 of my....1988.... Ashrae handbook (equipment).
    The Prof will have to root around the Sporlan archives for that Handbook sometime...
    Prof Sporlan

  22. #22
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    DOH!!!!

    Now, if I determine Mass flow, and required flow rate (5 lbs/hr) and the pressure drop is 1.5 psi per foot, I require 175 psia pressure drop.... maybe I should divide

    175 psia / 1.5PD/FT = 9.72' of cap tube....

    This makes things scary...

    Previously I had multiplied, not divided...

    Maybe Gary is back in the running with his 12' figure...

    ....

    PS.. Ihave digital pictures of my heat sink construction.... but I would have to have non-disclosure statements from anyone, before viewing.. hehehehehehe
    Last edited by herefishy; 04-06-2003 at 01:50 AM.

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    PS.. Ihave digital pictures of my heat sink construction.... but I would have to have non-disclosure statements from anyone, before viewing.. hehehehehehe
    That good... or that bad?

    I'll show ya mine if you'll show me yours.

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I think this might work for sizing cap tubes:



    Sections of cap tube separated by access tees. Altogether 10ft. Connect A to B bypasses 1 ft. Connect B to C bypasses 2 ft. And so on.

    When you get the right length, pull the testing rig out and install the right length cap tube.
    Last edited by Gary; 04-06-2003 at 03:47 AM.

  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Hmmmm... should add a 5ft section to make it more versatile.

    Could make those sweat tees, run a piece of tubing between each, with a shut off valve for each section.
    Last edited by Gary; 04-06-2003 at 04:58 AM.

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35


    There... that's better.

  27. #27
    Join Date
    May 2002
    Location
    The Netherlands
    Age
    48
    Posts
    274
    Rep Power
    22
    Originally posted by Prof Sporlan
    But it would hardly be appropriate for the Prof to be developing a cap tube selection program.. [/B]
    Put some effort in developing small 1/16 ton valves which operate down to 10% of rated capacity first

    But Prof, as usual I am very interested in that Excel sheet and the correlations used. I might be willing to write the captube selection program....

    Also a useful tip: Tecumseh / L'unite Hermetique has a compressor selection program which was also capable of calculating captube sizes given a certain compressor, condensing temp, subcool, superheat and load. The program was called DISK UH (DISK_UH.ZIP). A quick Google seach did not show the link, but with some browsing it should show up.

    What I did: I selected a compressor that matched the one I was using and ran the captube calculations. When it came up with some odd diameter, I used a mapping table to convert ID #1 to ID #2.

  28. #28
    Join Date
    May 2002
    Location
    The Netherlands
    Age
    48
    Posts
    274
    Rep Power
    22
    Originally posted by Gary
    image
    There... that's better.
    Make it a binary system by doubling the lengths of the captube. Thus: 1ft, 2ft, 4ft, 8ft, 16ft.
    This allows selection of the tube lengh up to 31ft with increments of 1ft. Say we need 5 ft, we would dial in the 4ft and 1ft section. If we need 27ft, we would dial in the 16ft, 8ft, 2ft and 1ft section.

  29. #29
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Make it a binary system by doubling the lengths of the captube. Thus: 1ft, 2ft, 4ft, 8ft, 16ft.
    Yep. That works.

  30. #30
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    I thought that you could not "break" the cap tube in such a manner, that it must be one continuous tube to even represent proper operation.

  31. #31
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I suppose the turbulance in the breaks could cause some small friction-like loss, but that would seem very minimal. I could be wrong.

  32. #32
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    I NEVER repair a broken expansion capillary tube (splice with 1/4" copper say), I always replace the entire critter.

  33. #33
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Me too. But we are not talking about repair, we are talking about saving countless hours of trial and error sizing adjustments.

    Perhaps Prof Sporlan could provide some insight here

  34. #34
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Hmmmmmm...



    Lose the handles. Recessed allen stems. 1/4 flare cap for each. Wrap the cap tubes around a piece of tubing. Insulate.

    Voila!!! The universal cap tube w/ suction/liquid HX.

    Wanna hire me, Prof? I think I can take this idea one or two giant steps further.
    Last edited by Gary; 04-06-2003 at 07:46 PM.

  35. #35
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Voila!!! The universal cap tube w/ suction/liquid HX.

    Wanna hire me, Prof? I think I can take this idea one or two giant steps further.
    The problem the Prof sees with this device is it will probably cost more to make than a TEV, and OEMs who use capillary tubes aren't generally keen with TEV prices as it is.
    Prof Sporlan

  36. #36
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Maybe. Maybe not. A TEV is far more complex. If you built one by hand it would cost a fortune.
    Last edited by Gary; 04-06-2003 at 11:55 PM.

  37. #37
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Sorry to come in late on this one, I've been out of the loop for a while.

    Looking back over an old thread on cap tubes reminded me of the Electrolux site which has some data on cap tube sizing which may be of use...

    It also has some tables for R12/22/134a/404a.

    Try this link -
    Electrolux
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  38. #38
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Well, now Mr Brian_UK......... "JUST WHERE IN THE H*LL HAVE YOU BEEN?"

    This darn thread has been goin on for a WEEK!!!

    That link is most very highly appreciated......

    My cuthtomer left with his prototype thrown together video card chiller.

    Hey, Gary..... just to let you know... I ended up putting about fourteen inches of 1/4" tubing in the 64' of .031" cap tube and put 27 crimps in it......... LOL!!!!!!! ROFL!!!!!!!!!

    I had a 205psig discharge, 5"Hg vacuum, and the screwed up thermometer we were using (not my fluke) that is mounted into the evaporator was reading -50F to -53F.

    We had a card attached to my evaporator block, so I kinda conclude that we loaded up the system just a bit.

    Also, I had three coils of 20' each cap tube which I tie-wrapped all together..... which I think helped.

    We know the compressor really sucks for the application...... so we're just going to overclock the video card and let the compressor fry!!!! LOL

    While Donebalp is having fun blowing the thing up, I am going to research a proper compressor/expansion device application for our new set-up.
    Last edited by herefishy; 06-06-2003 at 03:46 AM.

  39. #39
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Hey, Gary..... just to let you know... I ended up putting about fourteen inches of 1/4" tubing in the 64' of .031" cap tube and put 27 crimps in it......... LOL!!!!!!! ROFL!!!!!!!!!
    Have you thought about a hand expansion valve??

    While Donebalp is having fun blowing the thing up, I am going to research a proper compressor/expansion device application for our new set-up.
    I think I would go for a 1/2-3/4hp methanol chiller with a TXV. Maybe a modified window A/C. Then run waterblocks to everything.

    For a second project, I would build a small cascade low stage with a direct die block for the CPU. The chiller would be the high stage for the cascade unit in addition to cooling everything else.
    Last edited by Gary; 06-06-2003 at 01:17 PM.

  40. #40
    Join Date
    May 2002
    Location
    The Netherlands
    Age
    48
    Posts
    274
    Rep Power
    22
    A bit offtopic, but for me it is great fun to see you guys breaking your heads over the problems of such small-scale refrigeration.

    When I came here first, many of you thought I was insane, and recommended me to just buy a faster processor.

    Herefishy: you might want to check out phase-change.com. For professionals it is always good for a good laugh and a bit of head-shaking, but you might find some useful information about overclocking related refrigeration.
    Not to mention that a second knowledgeable professional could prevent Gary from getting overworked
    Last edited by DaBit; 06-06-2003 at 09:13 AM.

  41. #41
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Originally posted by herefishy
    Well, now Mr Brian_UK......... "JUST WHERE IN THE H*LL HAVE YOU BEEN?"
    Sorry,... family illness, having to work for a living doing assorted hours.

    Oh you know what we're like, whinge, whinge, whinge.

    Anyway, glad to be of help.

    Brian
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  42. #42
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Apparently, the prommie uses roughly 68" of .7mm cap tube.

    Going by the electrolux chart for R134a, they are aiming for just under 150 watts of cooling.

    Switching to the R404a chart, we would need about 3 meters of .7mm cap tube for the same wattage (at a lower temperature).

    The .7mm cap tube equates to just slightly larger than .026 inches (.0276), therefore to achieve the same effect we would want to go slightly shorter in length using .026 cap tube.

    In any case, 64 feet of .031 just doesn't make sense.

  43. #43
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    I just bought 100' of .028" cap tube. ;-)

  44. #44
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I wonder if a small needle valve (hand expansion valve) wouldn't be just the thing to fine tune it with.

    Henry Valve Co makes a 1/4 ODS hand expansion valve. 6291N is the number.
    Last edited by Gary; 09-06-2003 at 11:40 PM.

  45. #45
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    The "manual" expansion valve "is" an idea. I'm starting with 12' of .028 (got a vacuum on it as we speak).

    Gary, I might have to buy some of your books! (for the input)

    LOL.

    (I've got a good apprentice who needs it).

    see ya'

  46. #46
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    175 psia / 1.5PD/FT = 9.72' of cap tube....
    I think I may have found a problem:

    175 / 1.5 = 116.67

    Better buy some math books, too

  47. #47
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    DOH!!!!!!!!!

    .... and you thought 64' was crazy...............

    This compressor sucks (for the application) My swing was too high with the R-404A.... I charged R-401A and kept a card temperature (other side of the processor on the video card ) of minus 3C to +1C. very stable, and properly charged with up to 142 fps on the 3D benchmark program..... however, I think we're looking for better than that... tommorow I'm buying a Danfoss NFX10....

    see ya'
    Last edited by herefishy; 10-06-2003 at 04:12 AM.

  48. #48
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Correction on information provided earlier:

    The uncoiled and measured length of the prommie cap tube is 96 inches (of .7mm ID).

  49. #49
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Hi Gary,

    I hooked up 12' of .028". That copeland 1/4 horse rated at -40 R-12 250btuh was just not doing the job.

    My vendor with the Danfoss NF10FX compressors couldn't sell one to me, because the pallets of compressors were already sold to Coca-Cola. DOH!

    I selected a Tecumseh rated at about 870btuh @-10FSST R-134A, and employed it with the 12' cap tube and R-404A. The compressor was very happy.

    whilst running the benchmark program, the backside of the video card never got over 15degF and I had a suction return temp of about -34F running around a 5"Hg vacuum.

    Before booting the computer, I had chilled through to the other side of the card (other side from the evaporator/processor) to -18F
    Last edited by herefishy; 11-06-2003 at 03:40 PM.

  50. #50
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    That's much better. I'm beginning to think that about 8' of .026 with R404a is the ideal for these.

    Your superheat is 23F under full load. I wonder if it might flood back a little under minimum load?

    BTW, did you get those cheap guages calibrated yet?
    Last edited by Gary; 11-06-2003 at 07:43 PM.

Page 1 of 2 12 LastLast

Similar Threads

  1. oxidation scale in copper tube and fittings
    By DeB in forum Fundamentals
    Replies: 8
    Last Post: 23-06-2006, 09:45 PM
  2. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  3. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM
  4. Help to calculate Heat Exchancger
    By Carode in forum Fundamentals
    Replies: 1
    Last Post: 17-12-2003, 10:57 PM
  5. Tube staggered/squared
    By bersaga in forum Fundamentals
    Replies: 2
    Last Post: 05-01-2003, 11:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •