Thread: Tk Sr2 Code 26
11-02-2008, 05:27 PM #1
Tk Sr2 Code 26
hey all
i went to a tk toptech class a while ago and did not get this question answered you guys seem to be pretty smart
sr2 at a 50 degree box will code 26 after 15 minutes if td drops below 5.0
at a 10 box the td is even less before codes 26
i have downloads of units with a 8.0 td at 70 box
that code 26
im told that the td is now variable for different box temps
does anyone no the formula tk uses on the sr2
i got that info from service eng.
thanks tkjimmy
11-02-2008, 09:29 PM #2
Re: Tk Sr2 Code 26
Good question,
When the unit is in engineering labs being tested TDs are being calculated along with unit performance.
There are many factors when considering what a normal td is, such as:
Model of unit.
Optional etv.
Modulation.
Air chute
Optiset modulation temp bands, based off floor limit.
Cargo not loaded correctly causing short cycle.
If you are getting a code 26 which is low capacity, is it doing it in heat mode or cool mode?
There is no simple algorythim to figure out what your asking.
You need to send me that down load, so i can see what the S/W revision and compare all the TD data against the additional data offered in technican mode.
12-02-2008, 05:19 PM #3
Re: Tk Sr2 Code 26
not sure how to send other than email
12-02-2008, 05:33 PM #4
12-02-2008, 08:14 PM #5
Re: Tk Sr2 Code 26
From the download I am seeing quick temp pull downs, from 80 degrees f to Zero degrees quickly, This would indicate a couple things, loading while unit running at well sealed frozen dock, or short cycling, from bulk head or product improperly loaded.
I am ruling out compressor capacity and or other refrigeration related components based on the unit quick temperature pulldown. with ambient temps exceeding 80 degrees F.
Here are some items you should look at or possibly be concerned with as well make the customer aware of.
- What is the trailer dimensions?
- Do they use divider bulkheads? If so where is it set In reference to length of trailer.
- Do these units have return air bulk heads?
- What is the product they load?
- Do they load product off the floor?
- Do they load product too high?
A-Z
13-02-2008, 10:24 PM #6
Re: Tk Sr2 Code 26
tkjimmy,i would be thinking it has to be in your optiset programiing, i take it your talking in F not C so id expect a much greater td at those box temps, or your etv is not opening fully?? do you know the software revisions and what units are you having the dramas with?? SB or SL This all comes into it, let us know ok
14-02-2008, 01:06 AM #7
Re: Tk Sr2 Code 26
Daniel, I agree that optiset and ETV has an influence on TDs, but not in this case.
If it were an optiset controlled TD, it would not produce an alarm code for capacity as this is the way the unit is expected to run.
Based on the download I saw, I dont believe he has any capacity issues.. also unit its not equipped with optional ETV, so Fresh Set and etv problem are eliminated.
The download clearly shows from the time the unit is started at 80 degrees f till it reaches -5 degrees f is around 30 minutes.
Regards A-Z
lennox fault code
By richelli in forum Trouble ShootingReplies: 0Last Post: 01-02-2008, 09:13 PM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 10:23 PM -