Thread: Oil pressures
    55
    Oil pressures
    Hi guys, Have a system tripping out on low oil pressure.
    But when unit running,oil temp is 40.2degC
    And oil pressure is betwen 4.5 & 5.5bar.
    Thinking i could have a dodgy sensor???
    Apr 2001
    79
    5,071
    35
    Re: Oil pressures
    Something else to look for:
    Some systems are wired such that the oil pressure switch can be energized when the compressor trips on internal overload. Then the overload resets itself, but the oil pressure switch does not.
    This can make you think it is an oil problem when in fact it is a compressor overload problem (low voltage, undersized wiring, burnt contacts, loose connections, etc...).
    Check the voltage at the compressor with the compressor running.
    Oct 2006
    1,843
    21
    Re: Oil pressures
    Quote Originally Posted by N.Lewis View Post
    You say 4 to 5b oil pressure. Is that oil differential pressure?
    If you have 5 b then pump seems ok but you say sensor! What type of oil switch is it because some
    measure the difference in pressure and some use sensors. If it is electronic then yes the sensor or the switch could be faulty.
    We need more informations.
    taz.
    Aug 2007
    Adelaide Australia
    70
    562
    Re: Oil pressures
    Another thing you may want to check is that the oil failure switch is last in the safety control circuit. If the LP cutout is after the OFS every time the compressor shuts down on LP it will trip the OFS. Paul
    55
    Re: Oil pressures
    Hi guy's, as always thanks for all prompt replies and helpfull information, sorry it's taken so long to reply.
    To keep you posted, have replaced the oil pressure switch and sensor, unit is now running-cutting in and out.
    Again thanks to everyone.
    Nick.
  1. Pressures at Evaporating & Condensing Sides
    By stephen.t in forum Technical Discussions
    Last Post: 31-01-2008, 12:34 AM
  2. Hitachi pressures off the scale!
    By ianybeany in forum Air Conditioning
    Last Post: 26-04-2007, 09:42 PM
  3. Running Pressures!
    By G_Young in forum Air Conditioning
    Last Post: 16-11-2006, 11:00 AM
  4. System Design Pressures
    By herefishy in forum Fundamentals
    Last Post: 27-01-2004, 12:31 PM
  5. condensation pressures
    By abcdefg1675 in forum Refrigerants
    Last Post: 25-07-2002, 02:18 AM