Thread: Insulation
-
08-02-2008, 01:41 PM #1
Insulation
Can any body give me the
1. comparision chart of the recomended insulation at different temperature.
2. Suitable thickness chart for EPS and PUF.
regards,
-
08-02-2008, 07:22 PM #2
Re: Insulation
Hi!
You may find the information (including selection program) on
http://www.armaflex.com/www/armacell...e?OpenDocumentLast edited by Brian_UK; 09-02-2008 at 12:49 AM. Reason: Allowed url.
-
09-02-2008, 05:44 AM #3
Re: Insulation
R u talking about Cold stores? You have to follow Ashrae reco wherein recommended R values are given
-
11-02-2008, 06:57 AM #4
Re: Insulation
I want to know about the thickness required for cold rooms?
-
11-02-2008, 11:52 AM #5
Re: Insulation
Try asking the manufacturers. They would be having it.
-
11-02-2008, 01:01 PM #6
Re: Insulation
In India, use 125mm Thk PUF / 200 EPS for -25
use 80mm thk puf/ 100mm thk EPS for Chill rooms
& 60mm thk PUF / 80mm EPS for Processing halls.
Again based on the heights, only for structural strength you may have to go in for thicker panels!!!