    Evaporative condenserīs liquid drain trap



    Hi guys,

    Everybody knows that itīs necessary a trap in the liquid drain evaporative condenserīs piping when there are more than one condenser operating in parallel.

    We have a main run piping 2,5m far from the condensers.

    Whatīs the better solution in your opinion: to make the trap as nearest as the main piping (trap with a small horizontal piping lenght) or the condenser (trap with with a big horizontal piping lenght)?

    Best regards,

    Volnei



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi volnei,
    doctors differ, patients die I would run the main liquid line feeding the receiver with a pitch to the receiver. Then run each of the condenser condensate lines with a pitch towards the main liquid line, trapping the individual condensate feeds as they enter the bottom of the main liquid line
    Any other sugestion folks, as this is a bit of a grey area
    Regards. Andy

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25
    We have a main run piping 2,5m far from the condensers.

    Whatīs the better solution in your opinion: to make the trap as nearest as the main piping (trap with a small horizontal piping lenght) or the condenser (trap with with a big horizontal piping lenght)?
    I am having a little trouble picturing your choices, volnei, but I would think the less pipe the better, if that addresses your question.

    I am assuming you are referring trapping that obviates the potential of liquid refrigerant logging in one condenser or the other. I would think any trap equivalent to the vertical depth of the condenser coils would suffice.


    doctors differ, patients die
    Any other sugestion folks, as this is a bit of a grey area
    LOL Andy. It is more than a grey area. Liquid return line piping is a black hole, loaded with apparent contradictions.

    Many manufacturers recommend that you size the liquid return line to permit sewer flow (insuring a layer of vapor above the gently sloped pipe to avoid vapor lock in the receiver, for example.

    Then they go ahead and recommend traps. Some others (including ASHRAE) advise adding a receiver vent line to get around the first contradiction. Of course there are always check valves to play with.

    I whacked my self on my head with this one in the old Fridgetech pages to no great satisfaction.

    I think the simplest and shortest is the bestest. I have seen too many installations where the cures caused more problems than if all good advice was ignored in the first place.

    Drop directly from the condensers to a level near their mounting surface, join the pipe to the main and be done with it. And yes, the receiver is ideally located below the condensers.

  4. #4
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    718
    Rep Power
    23
    Could soneone post an informative link for me to peruse, if it is not inconvenient? I am entirely unfamiliar with this subject.

    thanks in advance

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi Herefishy,
    sorry I tried to find the post on www.fridgetech.com , the one Dan mentioned, but to no avail
    Maybe Marc could post an url to it.
    Regards. Andy

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25
    Dang. I could have sworn it was on Fridgetech. I couldn't find it either. I know ASHRAE fundamentals and Carrier manuls deal with the theory as well as Stoecker's book. Also Hussmann manuals did. I could copy and fax pertinent pages, if anyone is interested.

    If I recall how the discussion started, it was something like, what if you have two condensers piped in parallel, what tends to happen when all the fans cycle off in one condenser and all the fans in the other are running? Or what can you expect to happen when you have differently sized condensers piped in parallel?

    The going theory was that you had to have a liquid seal of sufficient height to overcome any pressure drop differences between the condensers, or otherwise one would log with liquid while the other has insufficient condensing capacity to keep up, thus you lose the benefit of the combined condensers' capacity.

    I seem to remember it was a busy debate. Now I am worrying in my dotage if I was imagining it all. I hate when that happens.

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25
    Here's something from Heatcraft. For what it is worth.

    http://www.heatcraftrpd.com/Maintena...s/H-IM-43B.pdf

  8. #8
    Join Date
    Jan 2003
    Location
    Venezuela
    Posts
    58
    Rep Power
    22
    If you have some condensers in parellel, the liquid line got to be trapped individually. If not, you have the same pressure comming into the condensers, but if one of the condensers do not operate properly, and therefore have a very little pressure drop over the condenser, then the other condenser cannot have a bigger pressure drop (it cannot have a lower pressure comming out) and will therefore back liquid up in the coil, until it allmost work as bad as the other one.
    Or look at it this way; if you have a equalising line from the reciever to the inlet to the condensers, then you have the same pressure in the inlet to the condensers as in the reciever. You have a pressure drop in the condenser and therefore a lower pressure than in the reciever. Hmm, If you have a trap, then there will be a build a liquid column before the trap to overcome the higher pressure in the reciever, no trap, then there will back liquid up in the reciever.
    Saludos

Similar Threads

  1. Liquid Overfeed Systems
    By US Iceman in forum NH3
    Replies: 151
    Last Post: 08-03-2007, 06:34 AM
  2. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 03:29 PM
  3. Liquid trap
    By Herschmidt in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 13-08-2005, 11:39 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •