    Positon of tx valves



    Can anyone tell me if there is a problem with mounting tx valves upside down.I have done a job where the valve diaphragm is facing down and Im curious to know if this will affect the valves performance.



  2. #2
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    The position of the valve body does not affect operation. orientation of the element sensing bulb should be taken into consideration (mounted horizontally, or if vertically with the capillary coming out of the TOP of the bulb).

    In orienting the valve body however, the one thing you should pay attention to is that it is NOT oriented in a way that oil will accumulate in the Equalizer port in externally equalized valves.


  3. #3
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    herefishy gets a Sporlan 'ATTA-BOY'.

    Mounting the TEV upside down, in theory, should not present a problem. But the Prof would suggest avoiding this practice on internally equalized valves, particularly when installed on bottom fed evaporator coils. Invariably, the underside of the TEV diaphragm will fill up with oil and, even worse, debris.
    Prof Sporlan

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25
    what about distributors? have started up a couple of jobs where the installer was lazy and stuffed the TXV (SBFPE's) in the valve compartment of a coolroom evap using only pipe supplied with evap, to do this it left the valve positioned in a way that the distributor sat horizontally. I made him move it as under low loads (room unstocked and down to temp) the valve appeared to starve the top two evap passes, moved the valve/distributor arrangement and all was good... well as good as it can be with those valves - they're all over the shop!!!

  5. #5
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Since refrigerant flow thru the distributor is typically two-phase, you can sometimes find where distributor orientation affects refrigerant distribution, particularly when the distributor and/or tubes are a bit oversized.

    Orienting the TEV and distributor such that they feed vertically, up or down, is your best bet.
    Prof Sporlan

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    TX valve should always be fed from the bottom to aviod oil accumulation. Oil in an upside down valve will make it function "funny". Danfoss recommend in their instructions manual so.
    Distributor will be positioned down for an even flow of refrigerant
    to all circuits.

    CHEMI

Similar Threads

  1. Stainless steel valves
    By Tycho in forum NH3
    Replies: 5
    Last Post: 05-11-2008, 02:16 PM
  2. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Replies: 6
    Last Post: 14-04-2008, 01:47 AM
  3. Suction Stop Valves
    By frank in forum Air Conditioning
    Replies: 10
    Last Post: 02-08-2006, 11:04 PM
  4. Glycol water valves
    By eng_ab in forum Industrial
    Replies: 2
    Last Post: 03-06-2005, 09:15 PM
  5. setting of hand reg valves
    By ecclesk in forum Industrial
    Replies: 7
    Last Post: 21-04-2005, 08:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •