    Cooling Capacity



    I am wondering how to calculate kW output from an air conditioning system by using the running data. I think that perhaps I may need to use a PT chart or similar. By using superheat, subcooling, air temps etc, is there a way to calculate how many btus/kW are being ouptput ?

    Thanks


    a problem shared is a problem halved

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cooling Capacity

    Each capacity of an air conditioner can be obtained by following calculations and by measuring the temperatures of the suction and discharge air temperatures of heat exchanger with thermometer and applying psychometrics chart.
    Terms:
    Qcool Cooling capacity (kcal/h)
    Qheat Heating capacity (kcal/h)
    Qdry Drying capacity (kcal/h)
    i1 Enthalpy of suction air (kcal/kg)
    i2 Enthalpy of discharge air (kcal/kg)
    x1 Absolute humidity of suction air (kg/kg)
    x2 Absolute humidity of discharge air (kg/kg)
    t1 Temperature of suction air (°C)
    t2 Temperature of discharge air (°C)
    u2 Specific volume of discharged air (m3/kg)
    V Air flow rate of measured heat exchanger (m3/h)

    Formulas:


    [0,24= Specific heat of dry air (kcal/kg°C)]

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Cooling Capacity

    Thank You.
    a problem shared is a problem halved

  4. #4
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: Cooling Capacity

    You might want to look at this tool/toy.
    http://www.hvactool.com/catalog.php3...vac%20analyzer

    It looks handy but I wonder why I would need to make such a measurement other than to prove to a customer that their equipment is doing what it is designed to.

    I suppose you could use it get a quick reading of the systems perfomance then put this information on your yearly service sheet.

Similar Threads

  1. cooling capacity
    By Ahmed_LNG in forum Refrigerants
    Replies: 4
    Last Post: 13-05-2010, 03:25 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling Capacity For Carrier Model 06e 299
    By maguro4448 in forum NH3
    Replies: 2
    Last Post: 30-11-2007, 01:16 AM
  4. Standard of cooling capacity.
    By ckkdj in forum Air Conditioning
    Replies: 5
    Last Post: 03-09-2007, 04:17 PM
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Replies: 13
    Last Post: 08-02-2002, 11:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •