Results 1 to 13 of 13
    Jan 2008
    India
    14
    Co2 For CA Cold Store
    Hallo,
    Can we use Co2 in CA/MA store as a secondary refrigerant.By Using only Co2 pump not compressor.
    thk.
    rajgulati
    Jan 2008
    India
    14
    Re: Co2 For CA Cold Store
    I mean by cooling the co2 by ammonia and pumped it to the CA chambers.
    rajgulati
    Jan 2008
    India
    14
    Thumbs up Re: Co2 For CA Cold Store
    Is anybody has experince in pumping of Co2 in cold rooms
    India
    688
    We had done similar work with Kwality ice creams long back. Co2 handling is very very tough & unless one follows precautions things could be dangerous. TWO issues. Toxic levels & pr built up in the cold store. At present , I do not believe India is really geared up for such things
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, rajgulati
    Quote Originally Posted by rajgulati View Post
    rajgulati
    Please, can you explain something more.....CA-controlled atmosphere chambers-right!?.......and cooling with liquid CO2 what temperatures you have in chambers, goods....what is that for....benefits...and so...thanks
    Best regards, Josip
    Aug 2005
    5,302
    Can we use Co2 in CA/MA store as a secondary refrigerant. By Using only Co2 pump not compressor.
    Why would you want to do that? CO2 will have very high pressures in the expected temperature range for CA storage rooms.
    You would be better to use a normal ammonia refrigeration system, I would think.
    India
    688
    We had an enquiry on similar subject. The idea is that say for Banana Ripening chambers you retard the rate of ripening by introducing Co2 in the room. & incedently the Bananas were to be exported to Europe & ripening process was to be completed in that country. The concept was to minimise the damage of ripened fruit during transport. Few companies here were hooked on to this idea first. Infact those were fertilisers companies & they had Co2 as their by product. We worked with them for a long But eventually nothing came out. Though on paper the idea was excellent. They also tried few R& D efforts to find out the duration with Co2 etc in the cold store for various fruit wherein the ripening process gets retarded.
    Jan 2007
    Canada
    65
    158
    Quote Originally Posted by smpsmp45 View Post
    Actually, Co2 increase rate of banana ripening. Bananas are breathing and exhale the Co2. Banana room required certain ventilation to keep Co2 level at minimum to prevent ripening.
    India
    688
    If I am right Ethylele is used for speeding up the ripening process
    http://www.electronicscentre.biz/ele...s/page0010.htm
    Jan 2007
    Canada
    65
    158
    A while ago I worked on banana carrier. As far as remember, the technology to transport bananas was following:
    1. After loading, temperature should be pulled down as fast as possible to 13.3 degC.
    2. Temperature should be kept as close as possible to 13.3 degC. Acceptable fluctuation is from 13.1 degC to 13.5 degC.
    3. Refrigerated spaces should have limited ventilation to keep Co2 level below 0.1%.
    Split Croatia
    57
    6,151
    36
    Here are some data for banana ripening:
    http://tinyurl.com/2aav2k
    Aug 2005
    5,302
    Hey guys, we are getting off track on the subject.
    The poster is looking for information on using CO2 as a secondary refrigerant (similar to using a brine/glycol solution) and pumping it to the coils.
    At least I think this is what he is looking for.
    Jan 2008
    Uk
    80
    8
    Quote Originally Posted by Sergei View Post
    Bananas rooms need to be purged after 24 hrs of ethylene gassing to remove the CO2 produced by ripening. If you don't purge, ripening is inhibited. same applies to citrus de-greening. Go to our website ventech co uk & download the user manual & read page9
  1. Replies: 0
    Last Post: 07-12-2007, 04:50 AM
  2. Cold Store Racking Design
    By Ashley in forum Ye Old Wifes Tales
    Last Post: 06-12-2007, 10:58 PM
  3. Replies: 0
    Last Post: 26-10-2007, 11:10 AM
  4. Cold Store calc
    By borley in forum Tools and Calculators
    Last Post: 19-10-2007, 08:23 PM
  5. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Last Post: 16-11-2005, 11:23 PM