29-01-2008, 07:20 AM #1
VRV issue
Hi sirs
There is one 1000m2 office with glass wall. Plan to apply VRV for its air conditioning. Is it feasible to use ground source outdoor and VRV indoor?
I plan to use multi-scroll + fan coil unit(r22) for this application. I'm no experience with VRV system. Pls give me some suggestions and how difficult it is. How much the risk I'll take?
thanks
regards
LC
I hear...I forget;I see...I remember;I do...I understand
-
29-01-2008, 09:02 AM #2
Re: VRV issue
To my knowledge, there is only Mitsubishi Electric that do a ground source VRF.
Best thing to do would be to find a Mitsu rep in your area and speak to them..
-
29-01-2008, 08:58 PM #3
Re: VRV issue
Daikin also offer a water cooled VRV system that can be piped as a heat pump or heat recovery. http://www.daikineurope.com/news/items/water_cooled_vrv-wii.jsp some installations have used it in ground source application.
Obi Wan
-
08-05-2008, 01:45 AM #4
Re: VRV issue
I'm working for mits. elect. and in this market, only we have ground sourced vrf system, not daikin or else so you can ask to Mitsubishi Electric Britian
Similar Threads
-
r22 replacement issue -emergent
By Lc_shi in forum RefrigerantsReplies: 3Last Post: 02-01-2008, 12:10 PM -
electrical heating cable issue
By Lc_shi in forum New TechnologiesReplies: 2Last Post: 21-07-2007, 09:51 PM -
large refrigeration plant cooling tower issue
By Lc_shi in forum New TechnologiesReplies: 4Last Post: 25-03-2007, 01:35 PM -
hydraulic floor heating issue
By Lc_shi in forum New TechnologiesReplies: 6Last Post: 02-01-2007, 09:07 PM -
Air conditioning system cleaning issue
By Lc_shi in forum Legal-Business-MarketingReplies: 2Last Post: 24-08-2006, 03:03 PM