    Condenser Length Problem



    Hi everyone.I am an engineering student in bangladesh doing an undergraduate thesis.My thesis topics is to construct a refrigerator based on the principle of vapor compression refrigeration system.I have calculated the total cooling load.But i cannot figure it out how to calculate the length of the condenser and evaporator length based on the cooling load.Please some one help me.My designed compressor is .2 hp.Using capillary tube as expansion device and using R-12 refrigerant.



  2. #2
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: Condenser Length Problem

    R-12 refrigerant! wow thats a lot of money to wast.

    I think you need to ask Gary this Author of TECH Method Troubleshooting books.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Condenser Length Problem

    Hey Tony, remember he is only doing a thesis not actually constructing a machine.

    A lot of text books always have an R12 data sheet.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Condenser Length Problem

    Quote Originally Posted by tanveerkuet View Post
    Hi everyone.I am an engineering student in bangladesh doing an undergraduate thesis.My thesis topics is to construct a refrigerator based on the principle of vapor compression refrigeration system.I have calculated the total cooling load.But i cannot figure it out how to calculate the length of the condenser and evaporator length based on the cooling load.Please some one help me.My designed compressor is .2 hp.Using capillary tube as expansion device and using R-12 refrigerant.
    Why you said lenght? Did you mean capacity?

  5. #5
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Condenser Length Problem

    In order to size any heat exchanger u fristly u need to know under what catogary the HE is calssified/. Anyhow there are five equations derived form mass/energy conservations are used to calculate the condenser/evaportor size.

    1- Q = U A LMTD

    2- Q = m CP DT for a hot side

    3- Q = m CP DT for a cold side

    4- m = density * Ac * veocity for hot side

    5- m = density * Ac * veocity for a cold side

    AC = area cross section

    DT = temperture differnce

    LMTD = log.mean temperture differnence

    Too often, u can find five unknowns in those equations if they are more that u have to assume a pratical value for unknow parameter.

    Cheers

  6. #6
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Condenser Length Problem

    Is it air cooled or water cooled. You have to assume some parameters & that can be worked out. I know what it means at the time of writing a thesis. If you are considering air cooled condenser,

    1. Max ambient temp
    2. Heat rejection
    3. Velocity acorss the coil.
    Should be the parameters of assumption.

    Same for water cooled.

    There you shall have to consider the optimum veloecity for water & refer to Rheem charts etc to work out the Length.

    But the capacity what you are working on is too small for all these.

    I would suggest instead you should take some concrete example so that you can also mention the practical values based on some company catalogue. That shall have more weightage in the thesis that going in for only theoritical work.

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Replies: 4
    Last Post: 15-11-2007, 07:03 AM
  3. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 02:50 AM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. how to calculate the length of evapurator
    By heanboon in forum Fundamentals
    Replies: 2
    Last Post: 17-10-2001, 12:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •