    How to test TXVs' capacity
    see the picture,it is a test method of rating capacity for TXVs used in automobile air-conditioning system.but there is no superheat.i think there must be superheat to open a TXV,am i right?i am so confused and need your help.
    could you tell me the test method of TXVs'capacity you know?Thanks!
    Feb 2007
    2,473
    Re: How to test TXVs' capacity
    In your picture they are testing the capacity of a TXV, they are keeping it "manually" open by immersing the temp sensing bulb in water of a fixed temperature.
    I always found the easiest way to find a TXVs capacity is to take the details of it and look it up in the manufacturer's data book.
    Nov 2005
    211
    That would cause the TXV to go "wide open" unless it is MOP type.
    That method of testing doesn't look like a very good idea as it would cause floodback.
    Feb 2007
    2,473
    Aha,
    But if you look at the diagram, it's some sort of test rig and not a "system"...
  1. Refrigeration plant Hydro test
    By psrao in forum New Technologies
    Last Post: 09-04-2008, 12:05 AM
  2. R-407C and Coil Capacity
    By glabah in forum Refrigerants
    Last Post: 03-06-2006, 11:36 AM
  3. Capacity achievement
    By Hemant Anand in forum Industrial
    Last Post: 18-12-2005, 01:18 AM
  4. New Capacity Control Solution
    By embrown in forum New Technologies
    Last Post: 30-12-2003, 01:33 PM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Last Post: 06-12-2002, 05:11 PM